Dan !

Jamie_6
Jamie_6 Member Posts: 710
Question?



<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    The valves,

    and there are two involved, would be on the bypass line, and between the bypass tee and the boiler on the return side. The water follows the path of least resistance.
    Retired and loving it.
  • Terry H.
    Terry H. Member Posts: 73
    Jamie

    I don't know the whole story, just wondering. What are you trying to accomplish with the bypass?

    Terry H.
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    It's a high-volume system,

    like an old gravity system. The bypass allows the boiler to come up to temperature.
    Retired and loving it.
  • Terry H.
    Terry H. Member Posts: 73
    Then

    In this case the system side is taking advantage of the bypass, slowing flow through the boiler and the flow control valve is in charge of setting boiler's flow right? Would you set the flow control valve with one or both pumps running? This must be a high mass boiler.

    Terry H.
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    It's more about

    limiting than setting in this case, Terry. And it can be for any boiler. What often happens with the old gravity systems, or with any old system that has large-volume radiators, is that there's so much water in the system that it exceeds the normal 15% piping/pick-up factor set by the boiler manufacturers. The bypass tricks the boiler into thinking that it's operating within a more modern system because there's less water flowing through the boiler. It gives the boiler a chance to come to temperature and shutoff. Without the bypass, the boiler runs for hours on end and uses a lot more fuel.

    Yes, I'd set it with both zones calling.
    Retired and loving it.
  • Dan , I had the same situation yesterday

    There more pics under the topic - Old gravity conversion - . I piped the bypass into the return . Even with the bypass valve full open the return temp was pretty low , and the low limit would trip very fast . There are 2 returns in 1 inch copper , with ball valves on each . If I partially close both valves , the return temp will increase , giving me a longer run time on the circ ?
  • Wait !

    I think I might've thought like water for the first time . If I partially close the 1 1/4 inch purge valve on my return , the bypass will circulate water around the boiler - not through it , bringing it up to temp . But how do you know when it is closed enough ?
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    When it

    stops doing what it's doing. ;-)
    Retired and loving it.
  • Jamie_6
    Jamie_6 Member Posts: 710


    O.K.

    So I put one valve (1 1/4" in this case) between the supply and the return tee in the bypass? Then I fire up the system and throttle this valve to maintain a x degree between the supply and return?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • And you will need

    a valve between the bypass tee and the boiler , on the return pipe . You throttle this valve to force water through the bypass instead of the boiler . New found knowlege is great .
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    That's correct.

    Retired and loving it.
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    Dan, I don't see

    How the boiler would fire anymore with or without a bypass....assuming a cold start. Also, related to this,I have never figured out why one would want the boiler to run at the high temp limit.
    It seems to be saying to me, "let"s get the boiler up to its highest temp and least efficient operation as quickly as possible and then cycle on the limit so we can keep it operating at that inefficient temp as long as possible". A cooler heat exchanger is more efficient, within limits for noncondensing boilers, so why do we want to get the boiler as hot as possible as much as possible? Seems to directly contradict the purpose of outdoor reset... keep the boiler cooler and more efficient as much as possible.

    Attached is how I deal with low operating temp systems....P/S piping with Thermostatic mixing valve on the boiler return.

    Boilerpro
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    Your way

    is better, for sure, Dave. What the bypass does is give the contractor a low-cost way of keeping the boiler from condensing for a very long time as it tries to make high-limit. It just runs on and on and on. I'd choose P/S every time, but it's often done this way here in the East because it's in the boiler manufacturer's I/O books, and it does work. Not as well, but it does work.
    Retired and loving it.