Buderus 2109 question?
Bill Nye
Member Posts: 221
What if I have to run the boiler for heat and do not have an indirect tank installed yet. Do I move a dip switch or disconnect the tank sensor plug?
On a call for heat the boiler ran up to high limit but the heating circ would not go. I do not have the indirect yet and did not wire the indirect circ.[the heating pump will run if I disconnect it from 2109 control and power it from L1 so it is not the pump]
It is a long story but... it is a health care facility and they need heat even though it is June 2. I replaced the fwa furnace with a boiler and air handler today. I stayed, with my helper, until 7:30 to try and finish. Left w/o the heat on.
First buderus I ever did with an AFG. P.S. you need to jump TT on the beckett primary control. When you are tired you sometimes miss the basics.
On a call for heat the boiler ran up to high limit but the heating circ would not go. I do not have the indirect yet and did not wire the indirect circ.[the heating pump will run if I disconnect it from 2109 control and power it from L1 so it is not the pump]
It is a long story but... it is a health care facility and they need heat even though it is June 2. I replaced the fwa furnace with a boiler and air handler today. I stayed, with my helper, until 7:30 to try and finish. Left w/o the heat on.
First buderus I ever did with an AFG. P.S. you need to jump TT on the beckett primary control. When you are tired you sometimes miss the basics.
0
Comments
-
Try this Bill!
The attachment is for altering the resistance on your Amtrol thermistor to talk to your 2109.You will need to power your smart control,The violets will go to #1(tank sensor).The diagram posted is for a Honeywell R822D......you won't need this relay since the "Smart Control"is a switching relay.If you cannot find a 2K and 8K resistor a 2.2 & a 10K will suffice!Good luck.......it's alot easier to use a Buderus indirect:)Guess you know that.I found out along time ago.
cheese0 -
On the Buderus R2109 Control, if not using the DHW circuit, a jumper must be installed on terminal TS #1 and #2 (Page 9, bottom of page in the Installation and Operating Manual), and the dial for DHW should be turned all the way down.
I believe the "Smart Control" on the Amtrol tank uses a 10k ohm resistor which is what the R2109 and R2107 use. Disconnect the sensor wires from the "Smart Control" and extend them to connect into the TS #1 & #2 terminal in the R2109. When using the R2107 control, connect to terminal FB #1 and #2. The circulator for the indirect tank should be wired into terminals #24 and #25 in either control.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements