Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Venting Buderus GA boilers
Options
Ray Landry
Member Posts: 203
I don't have adobe acrobat reader, and don't have any buderus manuals offhand. I'm hoping someone here can tell me what the maximum vent length for a Buderus GA124#17 is, and how much footage do you allow for one elbow?
0
Comments
-
Download
the Adobe acrobat reader (it's free)from the Buderus site and read the manuals. This boiler has particular venting requirements and you'd want to know the details.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
The GA124/17 can be vented up to a maximum horizontal length of 50 feet. There are four manufactures of 3" stainless steel AL29-4C that are approved for use. Most of these manufactures equate a 90 degree as ten (10) feet. You may want to check with each manufacture if length is a concern.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements
