Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Munchkin Vision1, Boilermate?

Nick_11
Nick_11 Member Posts: 25
How Can the Boilermate WH-7L-DW be wired to operate with the outdoor reset and indirect Water Heater features of the Vision1 package?

Comments

  • Jim Eastman
    Jim Eastman Member Posts: 41


    Any indirect water heater can be piped into the Munchkin with Vision control if you follow the piping diagram. The temperature sensor normally is inserted into a well, but the WH7 may not have a well. I would attach the sensor on the bottom of the tank to get a good spot to sense the tank temperature. The WH7 only has a 3/4" coil, though. Make sure that you are getting enough flow through the Munchkin when the system is on DHW priority.

    Jim Eastman
  • Guy_5
    Guy_5 Member Posts: 159



    Use the wires (Purple, I believe) that Amtrol provides , and attach them to the two blue wires for the aquastat in Vision 1. This will allow the Boiler-Mate the benefit of Vision 1 priority. You would set the temperature by way of the Amtrol Smart control, and not the Munchkin display. It will simply act as an on/off control.


    Guy Woollard
    Heat Transfer Products
This discussion has been closed.