Need panel insulation for boiler.....Boilerpro

Boilerpro_3
Boilerpro_3 Member Posts: 1,231
I have a Dunkirk D-247 with the exposed collector/drafthood and I want to enclose the collector in insulation. This is to help reduce the boiler room temp. I was thinking of just installing a sheet metal box lined with insulation, but need a source for the insulation. I am not sure if standard home fiberglass insulation is rated for the 350 to 400F temps of the collector.

Any suggestions? Will chamber liners set up under these conditions?

Boilerpro

Comments

  • Robert O'Connor_6
    Robert O'Connor_6 Member Posts: 299
    Well Dave

    first off, it was great to meet you at Wetstock!!


    Secondly it's critical to get the right stuff, I had a dry base boiler that would start stinking after 45 minutes of run time. I got the rep out there and he made a few phone calls. Turns out they got some off spec insulation at the plant.

    Sorry I don't know what the right stuff is., I'm sure you have called Dunkirk?

    regards

    Robert

    ME
  • John@Reliable_9
    John@Reliable_9 Member Posts: 122
    This works for me..............

    Just like you were thinking, but use Lynn fiberboard about 1" thick. I get mine from Lynn Products,the real use is for combustion chambers so temp. isn't a problem and comes in many sizes. John@Reliable
  • Maine Ken
    Maine Ken Member Posts: 531


    Comes in many thicknesses!!!!
  • Constantin
    Constantin Member Posts: 3,796
    Don't use home insulation!

    ... the stuff starts to decompose at 450°F, the binder catches fire around 500°F, at least according to a colleague who managed to set his lab on fire that way.

    Just because the collector only gets to 300-400°F under normal conditions does not mean it won't go higher under abnormal ones. Stick to the appliance-grade fiberglass at the very least (1000°F and above), you can order sheets of it from McMasterCarr if needed.
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    It was great meeting you too

    And hope you are having a good year!

    Dave