Munchkin Vision 1 Heating/DHW piping
Cliff Brady
Member Posts: 149
With all the talk of pumping into the boiler on Munchkins, I am curious why the Vision 1 piping diagrams have the heating pump P1 pumping into the boiler while the DHW pump
P2 pumps away from the boiler and into indirect tank?
Any comments?
P2 pumps away from the boiler and into indirect tank?
Any comments?
0
Comments
-
i would venture
to guess that you usually need around 10 GPM through the DHWT heat-x and there is very little friction loss as the piping is usually 1" or larger. so the DHW circ is pushing enough flow through the munchie heat-x.
leo g
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
From experience
I would not use the combi cor water heater with the schematic as shown. combi's have a way too high head loss. Plumber has one with a 140 and combi and even using a 0013 pump it will not move enough water to keep the 140 from complaining.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements