Need Help on Tank Vault pls

Einsiedler_2
Einsiedler_2 Member Posts: 93
Gentlemen - would appreciate your input on the following scenario...

Customer building small home on acreage c/w a tank vault buried underground. size of vault = 9'x24'x6'high. residing in this vault are 3-only 350Gallon cold water Storage Tanks...

He wants to lay 1 loop of pex-al-pex under tanks to keep temps above freezing.. I am concerned with the load vs out put of 1 loop. I am thinking it would be more prudent to line perimeter of room with radiation/baseboard...

Just not sure just how bad the load is with these tanks.
any thoughts?

thanks in advance,
EINSIEDLER

Comments

  • Einsiedler_2
    Einsiedler_2 Member Posts: 93


    *bump..*
  • Tony Conner
    Tony Conner Member Posts: 549
    If The...

    ...vault is buried below the frost line, do you need any heat at all?
  • Mike Kraft_2
    Mike Kraft_2 Member Posts: 398
    agree with...............

    Mr Conner AKA the mule skinner:)I have a small community that have several tanks in a vault.Freeze has not been an issue.

    cheese
  • Einsiedler_2
    Einsiedler_2 Member Posts: 93


    thank you gentlemen..
    thats what I needed to know.. I won't worry bout any Load for this vault then...

    appreciate your input(s) once again.
    You all have helped me & others considerably over several heating issues..

    sincerely, your Northern Neighbor...