I'm bidding a poll barn which requires 19,000 BTU's of heat & I was curiuos on what you guys think the best heating plant for this application would be?

The barn will be for a work shop. I am planing on using a 30% glycol mix also.

We have oil, propane, & electric available.

Jamie

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Murph'_5
    Murph'_5 Member Posts: 349
    We did small shop

    with gas WH with an exchanger to keep anti-freeze to a minimum, only had to spend the cash once! You may also get your domestic hot from here with this arrangement!!



    Murph'

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Art Pittaway
    Art Pittaway Member Posts: 230
    Hi Jamie,

    I'll probably get flack for this, but with the load, I assume it is a rural out building, and LP is available, the easy install is a water heater. No controls, just a thermostat and pump, design it for 90F supply temp and once it is at temp it will be fine. Snow melt 1'+ of your door aprons so ice doesn't build up and freeze the door in place. If it is a power vent, relay the thermostat to drop the W/H power off instead of running it all the time, (instant buffer tank?). Understand out how it is wired internally. They allow W/H for heat in Illinois but not Wisconsin, check your local code to see if W/H are permitted. Next choice would depend on price of fuel, some electric areas are very cheap so a small electric boiler (W/H?), and last is the oil if you want the service business.
  • Dale
    Dale Member Posts: 1,317
    Mats

    With only 19K needed and glycol needed I would look at electric mats under concrete if you are going to keep the space warm and not need a quick setback recovery, many rural elect coops have an off peak rate that might be applicable. My next choice would be a propane water heater.
  • hr
    hr Member Posts: 6,106
    A water heater if

    you still need to protect water heaters from extender condensation modes. I would highly recommend running 130- 140° and use a mix valve for the desired radiant temperature.

    Failure to protect the heater from extended cold runs usually presents itself a a burner covered in rust. A dangerous, CO producing mess!

    Dollar wise, a WH is a good entry level system for that size load.

    A small condensing Munchkin may be another option. The 50,000 modulates fairly low.

    A dual purpose water heater with a HX for the radiant is another option. Budget will dictate how much technology, and efficiency, can be had for that small load :)