Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
runtal radiators on(now pumped) gravity system
malcolmplumbing106435
Member Posts: 3
any comments on replacing cast iron radiators with Runtal radiators on a gravity hot water system with new boiler piped in a primary/secondary design with circulators?
Richard
Richard
0
Comments
-
I am in the minority on these things...
But I don't care for the cost, the look - or the output.
Unless I was doing an ultra-modern decor - I'd stick with the C.I. Radiation.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thermal mass...............
The steel will cool faster than the iron.
cheese0 -
Just like your new boiler is [hopefully] sized to the heat loss of the structure, you need to ensure that the panels are sized to the heat loss of the individual spaces.
If you size the panels at the 180° output of the standing iron, they're going to be similarly large and you're almost certain to have to use the convection enhancing models. Particularly if insulation/weatherization has been added the standing iron is likely WAY oversized--particularly on the highest floor of a mult-floor home.
Sizing will involve decisions--aesthetic, budgetary and performance related. TRVs and full reset will be very desirable. Try to use as many of the non convection-enhanced models as possible, but be aware that they absolutely cannot be covered by furnishings, draperies, etc. Panel rads must be considered part of the decor themselves.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements