High moisture content
Nron_9
Nron_9 Member Posts: 237
have to trinity boilers side by side with about 10' 2 abs pipe each for venting system , we are having a large amount of water vopor out of the units and is cousing the side of the house to ice up , this as you can emagine is making the home owner quite unhappy and were at a loss as what to due to eliminate the moisture problem , they are running 3 seperate unico systems and require a higher temp for the fan coils
  • don_35
    don_35 Member Posts: 1
    How
    close is the intake to the exhaust?You may need to seperate
    the intake and exhaust 18" or better.
    Appeal to me you have some mixing of air going on there.
    Let me guess it a concentric vent kit.Oh so pretty, but not
    made for cold climate.Hope this helps.
  • Nron_9
    they are seperate vents and the issue is when its cold the moisture from the gas is condensing on the ouside of the house causeing the ice todamage the sideing , the boilers are running fancoils and domestic water no radiant in this one and its the higher boiler temp that were seeing so much moisture about 1 gal for every 100 mbh and we have 300mbh in total with the two boilers
  • Uni R
    Uni R Member Posts: 663
    high moisture content
    Are the exhaust vents sloped back towards the boiler? Also, have you contacted NY Thermal? They might be the best source of information.
  • Nron_9
    yes i have the pipe is slop0ed at 1/4 per ft back to boiler and still get a lot of exaust gases from system
  • Ranger
    Ranger Member Posts: 210
    This just in...
    There is a new concentric vent termination approved for use on existing and new T150 & T200's as of 5-1-04.(existing York P/N:1CT0303, NTI P/N:82666).NTI has a down-load demonstration manual on proper installation of the product.