Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Underslab insulation testing
hr
Member Posts: 6,106
for comparing various under slab insulations.
I took a 18" square of 1" Dow foam, InsulTarp, and Refletix to a nearby ice skating rink yesterday. I put sensors between the insulation and some 4" thick concrete blocks I cast, were placed on top.
The ice was at 17°F, air temperature at 1 foot above the ice at 38°. I warmed the concrete blocks to 68° in the shop the night before, wrapped them in InsulTarp for the treck to the ice.
Interesting results. Think I may run an overnight test, and adjust my test rig a bit. Even with the sensors bonded to some copper the Tarp and Refletix softness allowed the sensor to get pushed into the material. I may notch the sensors into the concrete.
Thought about re-running the test with all the bubbles popped in the two bubble products, just for grins.
Any other thoughts or ideas. I'll shot for a Tue night retry, as the ice comes down Wed. for the summer in this rink.
I also tried a seat of the pants test after the concrete was removed!
Wish I had a data logger, be nice to watch the results for a 24 hour period, minute by minute. Gets cold standing around in there for hours :)
hot rod
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
I took a 18" square of 1" Dow foam, InsulTarp, and Refletix to a nearby ice skating rink yesterday. I put sensors between the insulation and some 4" thick concrete blocks I cast, were placed on top.
The ice was at 17°F, air temperature at 1 foot above the ice at 38°. I warmed the concrete blocks to 68° in the shop the night before, wrapped them in InsulTarp for the treck to the ice.
Interesting results. Think I may run an overnight test, and adjust my test rig a bit. Even with the sensors bonded to some copper the Tarp and Refletix softness allowed the sensor to get pushed into the material. I may notch the sensors into the concrete.
Thought about re-running the test with all the bubbles popped in the two bubble products, just for grins.
Any other thoughts or ideas. I'll shot for a Tue night retry, as the ice comes down Wed. for the summer in this rink.
I also tried a seat of the pants test after the concrete was removed!
Wish I had a data logger, be nice to watch the results for a 24 hour period, minute by minute. Gets cold standing around in there for hours :)
hot rod
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements