P/S question - replace A with B ?
Steve_45
Member Posts: 39
Can I use this heat trap to eliminate the return side
check valves? (replace A layout with B)
check valves? (replace A layout with B)
0
Comments
-
Thge deeper the better
I'd run it down to the floor, if possible. Just cost ya some more tube.
I did a ceiling to floor 7' drop on a chronic over heating zone once. It STILL trickled enough to over heat over the course of a week. Big improvement, but I went back with a spring check.
PAP tube is great for making those drops, a nice smooth fitting free loop. Easy to insulate with un-slit foam pipe insulation, too.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
thermal loop
john Seg says a thermal trap must be atleast 18" deep0 -
Looks fine
on paper, but when you install it in the boiler room, it takes up a lot of space.
I did it once; simple check valve works better for me.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
P/S
Hi Steve,
I have missed some of the previous posts, so I'm not quite up to speed on your control design.
Are your 4 zone pumps going to run continuously in heating season? Do you have 1 or 4 thermostats? Have you read-up on the B&G ThermoFlow Control valves?
1) I have read that if you insulate a heat trap, that it will stop working as desired.
2) Is a Taco 007 enough pump for your primary loop?
i.e. A Munchkin M140 would require a 0010 pumping into the boiler.
3) Couldn't your crossovers be 3/4"?
4) Whats the purpose of the end crossover?
Good Luck BP
0 -
Bill,
Thanks for the interest. Any hints, corrections will be greatly appreciated.
I have missed some of the previous posts, so I'm not quite up to speed on your control design. Are your 4 zone pumps going to run continuously in heating season?
++ No, Only when area calls for heat.
Do you have 1 or 4 thermostats?
++ There will be 4 (2 downstairs apartment, 2 upstairs apartment)
Have you read-up on the B&G ThermoFlow Control valves?
++ Only what I have found on the web. Must of which relates to sales and general purpose. Im using them based on a suggestion to have flow control on the secondarys.
1) I have read that if you insulate a heat trap, that it will stop working as desired.
++ I hadnt planed on insulating the heat traps or an other pipes in the basement to help keep the basement a little warmer.
2) Is a Taco 007 enough pump for your primary loop? i.e. A Munchkin M140 would require a 0010 pumping into the boiler.
++ Based on info from the wall on specs I believe so.
3) Couldn't your crossovers be 3/4"?
++ Based on the what I have read as well as suggestions from the wall the closely spaced tees should reduce the secondary side by one size. Based on that I changed from ¾ to 1 inch crossovers.
4) Whats the purpose of the end crossover?
++ For a future addition. Just to make it easier later.
Good Luck BP
0 -
actually, the end crossover should be in the beginning,
Should be 1-1/4, and should have a thermostatic or electric control valve on it to bypass the system until the boiler temp is above 140 - unless you are using a condensing boiler.
if the head traps are 18" long they should be fine unless the return pipe is un-insinuated and in so cold a wall, that the dropping cooler water can gather enough speed to loop right through, being that you have a pump per-zone and restrictions arent a problem I would go with spring checks they are $14.11 in sweat @ http://www.plumbingsupply.com/valves.html
third section down on the page - titled "Bronze Spring Check Valves:"
the thermometers in your drawing I would make them watts DPTG3s temp and pressure tricators so you can get delta t and delta p they also come with ½ spring loaded o-ring shutoff so you can unscrew them without draining the system
I would also use a pair of flanges on the return side after the valve to that you can disconnect for service and make all the devices over there IPS instead of sweat, you can even use a B&G Check-Trol for one half of the flange pair which comes with a built-in spring check. Flanges leak less than unions and provide electric isolation as well, if you use fiber washers for the bolts and nuts0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements