P/S question - replace A with B ?

Steve_45
Steve_45 Member Posts: 39
Can I use this heat trap to eliminate the return side
check valves? (replace A layout with B)

Comments

  • hr
    hr Member Posts: 6,106
    Thge deeper the better

    I'd run it down to the floor, if possible. Just cost ya some more tube.

    I did a ceiling to floor 7' drop on a chronic over heating zone once. It STILL trickled enough to over heat over the course of a week. Big improvement, but I went back with a spring check.

    PAP tube is great for making those drops, a nice smooth fitting free loop. Easy to insulate with un-slit foam pipe insulation, too.

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Nron_9
    Nron_9 Member Posts: 237
    thermal loop

    john Seg says a thermal trap must be atleast 18" deep
  • Looks fine

    on paper, but when you install it in the boiler room, it takes up a lot of space.

    I did it once; simple check valve works better for me.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • DaveGateway
    DaveGateway Member Posts: 568
    P/S

    Hi Steve,

    I have missed some of the previous posts, so I'm not quite up to speed on your control design.
    Are your 4 zone pumps going to run continuously in heating season? Do you have 1 or 4 thermostats? Have you read-up on the B&G ThermoFlow Control valves?

    1) I have read that if you insulate a heat trap, that it will stop working as desired.

    2) Is a Taco 007 enough pump for your primary loop?
    i.e. A Munchkin M140 would require a 0010 pumping into the boiler.

    3) Couldn't your crossovers be 3/4"?

    4) Whats the purpose of the end crossover?

    Good Luck BP


  • Steve_46
    Steve_46 Member Posts: 10


    Bill,
    Thanks for the interest. Any hints, corrections will be greatly appreciated.
    I have missed some of the previous posts, so I'm not quite up to speed on your control design. Are your 4 zone pumps going to run continuously in heating season?
    ++ No, Only when area calls for heat.
    Do you have 1 or 4 thermostats?
    ++ There will be 4 (2 downstairs apartment, 2 upstairs apartment)
    Have you read-up on the B&G ThermoFlow Control valves?
    ++ Only what I have found on the web. Must of which relates to sales and general purpose. I’m using them based on a suggestion to have flow control on the secondarys.
    1) I have read that if you insulate a heat trap, that it will stop working as desired.

    ++ I hadn’t planed on insulating the heat traps or an other pipes in the basement to help keep the basement a little warmer.
    2) Is a Taco 007 enough pump for your primary loop? i.e. A Munchkin M140 would require a 0010 pumping into the boiler.
    ++ Based on info from the wall on specs I believe so.
    3) Couldn't your crossovers be 3/4"?

    ++ Based on the what I have read as well as suggestions from the wall the closely spaced tees should reduce the secondary side by one size. Based on that I changed from ¾ to 1 inch crossovers.
    4) Whats the purpose of the end crossover?

    ++ For a future addition. Just to make it easier later.
    Good Luck BP
  • Kal Row
    Kal Row Member Posts: 1,520
    actually, the end crossover should be in the beginning,

    Should be 1-1/4, and should have a thermostatic or electric control valve on it to bypass the system until the boiler temp is above 140 - unless you are using a condensing boiler.

    if the head traps are 18" long they should be fine unless the return pipe is un-insinuated and in so cold a wall, that the dropping cooler water can gather enough speed to loop right through, being that you have a pump per-zone and restrictions aren’t a problem – I would go with spring checks they are $14.11 in sweat @ http://www.plumbingsupply.com/valves.html
    third section down on the page - titled "Bronze Spring Check Valves:"

    the “thermometers” in your drawing – I would make them watts DPTG3’s temp and pressure tricators – so you can get delta t and delta p – they also come with ½ spring loaded o-ring shutoff – so you can unscrew them without draining the system

    I would also use a pair of flanges on the return side after the valve to that you can disconnect for service – and make all the devices over there IPS instead of sweat, you can even use a B&G Check-Trol for one half of the flange pair which comes with a built-in spring check. Flanges leak less than unions and provide electric isolation as well, if you use fiber washers for the bolts and nuts