Tacos' new Radiant Mixing Block
Ted_9
Member Posts: 1,718
I'm looking for reviews. I'd love to start installing them.
0
Comments
-
) I am WIth you on that one:)
so in the "advanced"tekmar control class what is the first Question outa my wouth when the instructor asked if we had any questions? you got it! "can you describe the operation of the new Taco pump block with the controller abd both pumps:)"?:)" he could see the interest was in all our eyes and Knew we werent going anywhere till we got an answer:)0 -
Taco Radiant Block Submittal Data, Instructions
Good Afternoon
Attached are the Submittal Data, and Instruction Sheet for the New Taco, Radiant Block. Hopefully, this will make you more familiar with this great new product.
Joe Mattiello
Technical Service TechnicianJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
I am impressed with the product
I am waiting for them to show up on my dock so I can send them back out the door. I have spec'd them on a few single zone, single temp jobs before I start on some larger projects.
The price point is pretty attractive for what equipment it "replaces".
Please note that the attached drawing is still a work in progress. I am playing with where I want to attach PRV, Expansion tank, and double-check.
Regards,
PR0 -
Thinking about a constant flow application
on my secondary loop.
I am thinking that in "Reset-mode", I can make the Maximum Supply and Design supply temps the same, and plug in my design room temp for my Minimum Supply temp?
Comments?, Ideas?
Regards,
PR0 -
this looks very much like
a pair of pumps - one for system a one for injection with and intergrated tekmar 361 - and air vent
question is, can it really handle more than 85kbtu with 3/4 connections - i just did a system manually like that but the primary and secondary was 1-1/4 and the injection was 1", for a baseboard load of 117kbtu 11.7gpm ?
and how have you eliminated injection ghost flow - i pumped down 18" from pri to sec to elemininate ghost flow - what does it do? or are the pumps IFC's and you depend on the spring checks?0 -
Buderus Quick-Fit Mod piping system
Paul Rohrs, is that a program your using for the piping diagrams?
Which one?0 -
Microsoft Visio
It is a very handy tool.
Regards,
PR0 -
yeah...but
you have some visio stensil components that i didn't find on the tekmar website - care to share?
otherwise we have to take the "Mixing Block's" jpg and re-draw it or try to scale it, which never looks right
if only ziggi would use visio - he uses a mac - and you know what mac users say, "you can only take my mac, after you pry my dead fingers from it"
i have redrawn his, in powerpoint which works just as well in visio - can email it to you - can't attach ppt or vss or viz files on the wall0 -
Stencils
Yes I have a few stencils, but I can grab any JPEG file or picture from the Taco, Peerless, and any other website and drag it into my Visio program to CREATE a stencil. That is what you are looking at for the Radiant Mixing Block, Taco pump, and Pinnacle boiler. You can make it as versatile as you want it to be, but it is an investment of time to set up.
It is especially handy for the electrical side and wiring diagrams. I am looking at contacting Taco for some of their components that I can dovetail into my drawings as well.
Regards,
PR0 -
for doing those
i use pain shop pro - since if you put the image into a layer then right mouse erase undoes erase - so if you clipped the edge of a pic while erasing, you can hold the right mouse button instead and go over it again to bring it back - real neat
perhaps we should just email all our stuff to dan to put in a section - but he might not want to get into the copyright issues0 -
why the outdoor sensor. Exquisite heat would be more comfortable.0 -
Anyone actually Buy one yet?
three nice radiant jobs to plug and play buh no mixin blocks around here0 -
Visio
Very nice work Paul, I always wondered which program you were using to prepare your drawings.0 -
External Pump Wiring Detail
I am a radiant floor heating system designer and am planning to use my first Taco Radiant Mixing Block on a project where radiant floor heating will be included with a small addition to an existing building. The heating contractor is interested in the product and sees this project as a good candidate for the RMB-1.
I plan to include an external boiler pump and was reviewing the Data Instruction Sheet for information. Page 10 of the Data Instruction Sheet talks about removing the line cord and hard wire the RMB. Also, a female spade connector should be added to feed the pump and the neutral run back to the neutral input power supply.
Since I am a designer and not an installer, I would like to provide this detail to the heating contractor. Is there an additional data sheet showing this detail or maybe a hand sketch that would detail the installation? I would appreciate any help with this detail
David Michaud,
Northeast Radiant Technology0 -
there is no reason to take out the plug
i do all my pumps with plugs - as long as you
have a GFI breaker or GFI outlet powering it - then it's
ok by the national or even nyc's electric code
it's such a great convenance to be able to disconect for service - or plug into an alternate power source like a Battery backup power supply
the best thing to do is to have the main line to the boiler go through a GFI continuing outlet - ie the ones that protect all the circuits following it - they make them with an indicator like to tell you if it's alive0 -
the radiant block is not much different from my setup
just more compact - in that the system and injection and tekmar are all rolled up in a neet package - but if you look at it, it's very similar with the sensor's input's etc
even the display on my 361 shows the similar stuff
my application happened to be baseboard - low-head-hi-flow opposite of what the taco was designed for
0 -
wiring multiple rmb's
Still unclear about how you would wire multiple RMB's with multiple temp . Ok,hi-temp circs,and dhw off taco's zone control relays like a sr504.
but how would you wire the pumps or zone valves on the supply side of RMB's. Another zone control panel?0 -
Send Taco pump blocks to Alaska......
Send Taco blocks to Alaska.... Send Taco pump blocks to Alaska... send NEW Green Taco ESP valves to Alaska ....Send the NEW Taco Green ESP valves to Alaska... soon the summer will butt heads with 60 70 below zero.. hurry up... I dont wanna Stress you guys just ship the things Willya?0 -
relay or contacts
if tstat drives pump realy, use another set of contacts or another realy to drive the demand input o the rmb
it useing ZV's use the aux sw from the zv's to the demand input
ps the demand input are the "com" and "heat/dem" terminals on the right - and can take powered or un-powerd input
powered=is live 24 volts - unpowered=just a switch -
you cant mix the two types of input !!!
a zone control board is probably your best bet if you not electronic savy0 -
RMB Availability
Hey...this is a really hot product!! Trying to keep up with demand is a challenge, that we at Taco welcome and will conquer. The logic in this control is not new; it is similar to the PC705-2 injection mixing control, used with Taco switching relays. The benefit of the RMB is having the injection pump, supply pump, and the control, bundled up in a neat package, facilitating piping, reducing time, and money. Currently, there are several hundred casting on order, and Taco management is closely monitoring the orders so every Taco, representatives receives product satisfying customer orders. Additionally, we have several orders for the new I series mixing valve, which modulates the flow, based on outside temperature. For your convenience I have attached information on this new product. This is a very exciting time for Taco. We have a great staff of engineers that listen to customers needs, and are designing products that is setting the standard.
Joe Mattiello
Technical Support Services
Tel. 401-942-8000 X 484
Fax. 401-942-2360
joemat@taco-hvac.comJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
Weezbo
Check with Ferguson in Anchorage (recently FNW or Alaska Pipe & Supply). I just got back from Rhode Island where we toured the TACO Factory and saw the RMB. I now have one on my desk and a job coming up where I will need 2. Don't know how many they have in stock, but check with them.
Pat Clark0 -
Tacos' new Radiant Mixing Block
I've got one thats going in a job soon. Cant wait to see it in action.0 -
Pat ! Ta KUuu.
Dave said hes send me one soon ..i got a home for three of them:) Ta Day! )0 -
Joe.!
are you the guy i tried to get to auction off the one you brought up here a bout 5-6 months ago? Man , You could have been Fishing for Halibut if you would have let go,at least, the Green ESP valve:)))0 -
Excellent Customer Service
No, you have me confused with Dave Sweet, Or Mark Chaffee, Product managers for the RMB, and the new I valve. They have been traveling extensively spreading the good word, about these new products. My position is to stay here and hold down the fort, and chat with you. Please feel free to contact me directly, if you have any questions, or concerns on any Taco related products. Taco is a Family owned business that cares about the customer. Joe Mattiello
Technical Service Technician
Joe Mattiello
Technical Support Services
Tel. 401-942-8000 X 484
Fax. 401-942-2360
joemat@taco-hvac.com
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
\"Family owned business \" - oops re-edited
cheeeeezz - must be run by the grandchildren by now - you guys have been around so long
any way - any diagrams for two or more in a system?
and is there any plan to offer this in a high-flow/low-head application such as fin coil convector?
also needed from taco is integrated block with two pumps and a flat-plate heat exchanger - so that it's easy to install isolated system - example - glycol snowmelt from reg heat or a radiant zone from a domestic hot water heater
of course the flat plate HX would have to come in sizes, and the pumps would have to interlock so that the snowmelt side doesnt run until the fresh water side is hot enough, not to freeze in the presence of super cold glycol on the other side it would make for such a neat install0 -
Joe, my apologies for raggin.....
I like taco,705-2's, it is .:( and such a perfect job . i've been procrastinating and every thing for over 6 months now. i long ago bought the expandable and the 501 for the stand alone system,i will go with the 4 way mix and call it good. everything comes to he who waits an i am just being impatient..still i shouldnt have took ta beating the willing horsey. i have no idea who is making the pump block for you,and let my mouth over ride my brain on the comment .0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements