Patented 1898

Dave Stroman
Dave Stroman Member Posts: 766
Hey heating guru's, what did I find? Looks like, and is piped like some sort of diverter tee. It is on a gravity hot water system. I want to add some raditors but not sure how it will affect the flow to the existing radiators.
And look at the poor boiler standing naked in the basement.

There was an error rendering this rich post.

Comments

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    That's the Eureka fitting, Dave.

    Look in Hot Water Q&A on the navigation bar and then look in Gravity Hot Water Heating. Scroll down to a cutaway drawing of it. Nice find!
    Retired and loving it.
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    And

    it pays to wander off the Wall. ;-)
    Retired and loving it.
  • Steamhead
    Steamhead Member Posts: 17,387
    Dave, when replacing that boiler

    use as small a circ as you can get away with, to mimic the gentle gravity flow so those Eureka tees will still work. Go to-

    http://www.heatinghelp.com/newsletter.cfm?Id=125

    for more on this. Yes, it really pays to wander off the Wall!

    If you want to add radiators, it might be best to run a separate loop and leave the Eureka-tee loop alone.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Dave Stroman
    Dave Stroman Member Posts: 766


    Thanks steamy, I will take your advice. Have you ever installed a new boiler without a pump? Just left the system gravity? I have run into a couple of them around here. Looks like they used a big Peerless with large 3" pipes.
    Dave Stroman, Denver

    There was an error rendering this rich post.

  • Steamhead
    Steamhead Member Posts: 17,387
    We haven't done that

    but there's a very small house down the street from me with a Burnham 406 installed that way. Seems to work fine, even though the tappings on the 406 are only 2-inch. But again, it's a really small house. If you size your circ just right, the system will behave almost exactly the way it did before, except that the rate of circulation will be constant regardless of water temperature.

    I'm not that familiar with Peerless, do they have tappings larger than 2-inch?


    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Robert O'Connor_6
    Robert O'Connor_6 Member Posts: 299
    The

    problem with installing a pin type cast iron boiler on a gravity system without a pump is that the boiler never gets out of condense mode.

    You really need to operate these boilers for only the briefest peiods at low temps.

    Thats why a circ and bypasss lets you get the boiler up to temp and control your circulation.

    Robert O'Connor

    ME
  • Dave Stroman
    Dave Stroman Member Posts: 766


    Peerless is a common brand for steam boilers around here. Mostly 2" taps until you get into the larger ones. The last one I saw had 2" near boiler piping that was nicly welded.
    Dave in Denver

    There was an error rendering this rich post.

  • Dave Stroman
    Dave Stroman Member Posts: 766


    I always thought that on a gravity system you did not need to worry much about condensation because the flow was so slow until the boiler started to come up above dew point. Or maybe it was because all these conversion burners were so over sized. We see only gas burners around here. I was on top of a tall brick chimney once when the old boiler was firing. I knocked some old mortar down the chimney and the draft was so strong the it blew it all right back in my face. I get asked a lot about how efficient these old things are. I guess about 50% but I really have no idea.
    Dave in Denver

    There was an error rendering this rich post.

  • eric legacy
    eric legacy Member Posts: 16
    Go pinless




    Ureaka!

    Tie it in primary secondary with only 1 circ. and 1 flo-check on the boiler loop. make your main system one big loop. size the circ for a 30F delta across boiler. I wont reccomend a reset control because your pickup time is too long. A tripelaquastat L8124A will work great.Set high to 180 and low at 110 with a 25 diff. The boiler will maintain temp all summer, 85 to 110 (110-25=85)this will prevent condensate from forming when relative humidity is high and nights are cool.(buderus boilers have little off cycle losses)It will also prevent condensate from forming during winter op. because pump will cycle off if boiler temp drops below 110F on a call for heat. With this set-up you will get a moderate amount of comfort and fuel savings. Vs. large savings and no comfort or lots of comfort and no savings. Do a fresh heat loss calc. and upsize the boiler 25%over actual heat loss (gross output+ 25%) due to your excessive piping and pick-up loss. Or even better Insulate the piping and use net IBR. (IBR=a 15% derate from gross output Based on a fin tube system.)

    If any one would like to comment on this set up , please do Dan H., are you out there?...........
  • Dave Stroman
    Dave Stroman Member Posts: 766


    I have used the aquastat idea before to keep the boiler above condensate temp. We do not have a high humidity problem in this part of the US. Powder dry. Not sure what you mean p/s with one pump. Just leave the existing loop gravity and use the pump on the boiler loop. ME and I have talked about doing this before but I have not tried it yet. Do you work for Buderus? Use lots of them.
    Dave in Denver

    There was an error rendering this rich post.

  • eric legacy
    eric legacy Member Posts: 16


    Yes I do work for Buderus.

    Whats your fax # Ill shoot you a drawing.
  • Dave Stroman
    Dave Stroman Member Posts: 766


    My fax number is 303 369 9737. Love to see a drawing.

    Dave in Denver

    There was an error rendering this rich post.

  • Mark Eatherton1
    Mark Eatherton1 Member Posts: 2,542
    Here,,,

    Now you'll know what the other person on the phone looks like...


    ME