Finding Twintran
Dave Larsen
Member Posts: 3
Have a customer that had Heatway Twintran installed about twelve years ago. Three leaks have started on one manifold,but whoever installed this only left about eight inches of tubing coming up from the floor. I need to make a couple of splices to replace the tube at the manifold. Talked with Heatway and they have splice kits but haven't made twin tran (1/4") for at least ten years ........any body have a scrap of this that they could part with?? Any response would be greatly appreciated!
0
Comments
-
How much
do you need? Do you have splice kits? Could you extend the manifold branch with copper tube?
I have some pieces. No warranty expressed or implied, however
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
3 ft
3 ft is all I really need! Don't want to extend with copper because its one of the old Heatway manifolds with ports 1" apart.......don't want to disturb the other ports! Heatway still has a few spilce kits so I'm covered there. Call me at 920 839 2211 and I'd be Glad to buy some Thanks!!0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements