Taco 007 Flow
DaveGateway
Member Posts: 568
Taco 007 pumping to 4X Honeywell 3.5Cv zone valves.
8" past each zone valve is a pair of 3/4" closely spaced t's supplying each zones 006 pump, very little resistance back to 007.
If only 1 zone valve is open, will the pump have enough head to lift any of the others?
Thanks
8" past each zone valve is a pair of 3/4" closely spaced t's supplying each zones 006 pump, very little resistance back to 007.
If only 1 zone valve is open, will the pump have enough head to lift any of the others?
Thanks
0
Comments
-
pumphead
add a pressure bypass valve in your loop to prevent dead heading the pump or wear on the zone valves
Nron
0 -
Taco 007 Flow
I don't know exactly what dead heading is, I think it means: pump on & nowhere for the flow to go through.
All 4 of the zone valve end sw. will go to a Taco SR501, that turns on the 007. How could it dead head?
Thanks0 -
Nron?
Did you make a career change. At least I'm hopful now the industry might be on a financial upswing. Any inside tips??0 -
Taco, 007
Good Afternoon
Thank you, for using Taco, products. The CV will provide the pressure drop required to calculate the system resistance. Additionally, we need to know the flow rate required, to determine what the net flow rate will be, using the CV, total length of pipe, and diameter. Please advise, if you require additional assistance.
Joe Mattiello
Technical Service Technician
Joe Mattiello
Technical Support Services
Tel. 401-942-8000 X 484
Fax. 401-942-2360
joemat@taco-hvac.com
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements