adjusting the Z dimension
jaybee
Member Posts: 128
How do u adjust setting on adjustable head Im not sure what is meant by always check zero settings to insure the tube is matched to the draw assembly and adjust if nessary? Does anyone have a picture of this or know where i can look to understand better?
0
Comments
-
adjusting Z dimension
How do u adjust setting on adjustable head Im not sure what is meant by always check zero settings to insure the tube is matched to the draw assembly and adjust if nessary? Does anyone have a picture of this or know where i can look to understand better?0 -
Jaybee, Here's how you set it on a Beckett M-Series Tube. I believe this will give you a better understanding of what the Z-Dimension is about.
Beckett Z-Dimension
Your friend in the industry,
Alan R. Mercurio
Oil Tech TalkThere was an error rendering this rich post.
0 -
thank you very much!!!!!0 -
There was an error rendering this rich post.
0 -
Z guage
there's a Z guage for beckett burners and not the
steel plate guage the Z guage, it's orange and plastic.
it fits on the nozzle, it's very simple all you have to do
is take the nozzle assembly out of the burner and slip
the Beckett Z guage on the end of the nozzle. then with the Z guage on, put the assembly back in the burner, loosen up the escusion nut 1/4' nut driver or flat head screw driver.
put the assembly in place through the escusion plate and push the assembly foward until it stops, tighten the escution nut and pull out the assembly and take off the Z gauge and put the asembly back in place and you're all set.0 -
This would
> How do u adjust setting on adjustable head Im not
> sure what is meant by always check zero settings
> to insure the tube is matched to the draw
> assembly and adjust if nessary? Does anyone have
> a picture of this or know where i can look to
> understand better?
0 -
This would
apply to an adjustable head like a Carlin and not so much a fixed head, like a Beckett F head.
If you change air tubes, the scale on a 98,99,100etc, or 201-1150 etc., may not match exactly. You would have to remove the burner and check to see if the "0" [zero] setting does in fact put the retention ring flush with the end of the air tube. If not you will have to adjust accordingly to compensate for the scale being off.
Some OEM air tubes may be a slightly different length than the standard replacement air tube. This is only a "reference" point for initial start up. Proper combustion testing should be done for final setting. You would set the air per the OEM application guide and move the head back and forth to fine tune for zero smoke and proper CO20 -
Steve..not for \"M\" tubes..back to Alans post
0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements