Honeywell smart ? valve
D lux_2
D lux_2 Member Posts: 230
Have a cust. with a Armstrong Mod GUJ125D20-2B Ser 8496H13878
new in fall honeywell smartvalve SV9502H 2704 44479_001
old SV9500H2724 Quit working
We replaced this valve last fall and it fails to light the burners in spring weather . It was ok in winter cold weather .He replaced the Plight and hsi yesterday still won't light every time .I havent been to the job yet he called in this AM and droped off a tape of furnace cycles 15 min long any ideas? All have to get the kids in bed so I can watch the tape THANKS FOR ANY Help
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=169&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
  • don_9
    don_9 Member Posts: 395
    it could be several thing...It sounds like to me that
    you'll riding the max on your temp rise and its going out on limit.
    I say this because it work find when there a load,and now spring is here you have a parcel load cycling out on limit.
    Check your temp rise at the furnace,if its riding on the high side I would make a fan adjustment.That is after checking for dirty filter and collaspe duct,gas pressure,
    this and that.
    I not sure if this is a condensing furnace,but if it is there was a service bullentin,where water from the draft inducer would drip down on the valve and mess up the circuit board in the valve.Can check for you tomorrow when I get to the shop.
    Hope this helps.
  • Will be going over that
    Smart Valve in seminar tomorrow. What is the Electronic Fan Timer or Integrated control used on this unit? Is there any LED code flashing on the electronic control when it fails?
    Was the replacement control from Armstrong or was it a Tradeline over the counter model? The reason I asked is that control cross references to a SV9502H2522, if I am not mistaken the original did not have pre-purge and the replacement does is this correct?
    I would also check the settings on the control as to fan times and possible limit cycling off due to poor return to supply temperature rise. The fan should continue to run if it is cycling on limit or if off on limit on a call for heat the fan would already be on. Most of these have a self-healing feature for fan operation if any of the limits open, blocked vent switch, flame roll out or regular limit. Also watch out for an auxillary limit in the blower compartment.
    The other thing to check is the hose from the inducer make sure it is in good condition and no moisture inside or algae, it is a good idea to flush it out with some water and then blow through it to dry it out and make sure it is clear. The hose should be as short as possible. Also watch the diaphragm action on the pressure switch to make sure it is making full contact and full break away on the pressure switch. They have been known to cause short cycling because they do not make full contact.
  • D lux_2
    Ok I watched the tape He made it at 3:30 AM The Plight lights the burners all come on they will stay on for a few sec. to 2:00 min and go out this cycles 5 to 10 times and some times it will stay on and blow heat. I dont see this as a heat rise problem or limit as the furnace is cold at start up . it seems weather or longer off cycles me come in to play . as best as I remember I bought a armstrong replacement valve . thanks for the response ..
  • Glenn Harrison_2
    Glenn Harrison_2 Member Posts: 845
    Service Bulletin for GUJ
    Hey DLUX, here's a service bulletin for your exact situation and unit.
    Hope it helps, Glenn
  • D lux_2
    hey Tim
    thanks for the fast reply whats the micro amps for the S V thanks
  • Hey Glenn, I am not getting
    that bulletin very clear could you fax me a copy.
    401-270-1893
    Tim
  • D lux the microamps
    for Generation II is a minimum of 1.3 microamps. It should be around 3 to 5 normally.