Buderus g215 - Venting question

John_41
John_41 Member Posts: 1
Just had 215-3 oil boiler installed w/F5 Riello burner. Installer stated that a barometric damper is not required for the vent, since it is 'postive pressure'. A 7" vent taps into a standard 10x10 clay lined masonry chimney. The chimney is about 20' tall(2 story house, no basement). The old WM had a baro. Anyone have thoughts on this?

Thanks

Comments

  • don_25
    don_25 Member Posts: 2


    I have seen some application where the damper was not needed.But here code require it if you need it or not.
    jmho.
  • Robert O'Connor_6
    Robert O'Connor_6 Member Posts: 299
    Well

    For openers I believe there is a slight positive pressure over the fire but that the flue will be negative. A barometric doesn't add draft it just controls it.


    "high pressure goes to low pressure"

    Local codes and the I/O dictate.

    However it may be that in a 20' chimney draft is marginal.

    I would put one in regardless . It willl stay closed if it's not needed. And on those cold winter days when it may be needed you'll get good starts from that Riello. Riello's really like a zero to slight pressure in the fire box and a draft regulator will give it to you every time.

    Robert

    ME