The boiler is a W/M with a Beckett AFG and Field Controls outside air kit on it. The chimney is masonry and at least 40' tall, with most of it inside the home. The question is -- There is a tremendous amount of air flowing thru the boiler when it is not running, there by increasing the standby loses. Any thoughts on how to control this? Thanks.
0
Comments
-
controlling combustion air
Beckett makes an "inlet air shut-off" part #5861. This will stop any air from going through the burner.0 -
careful there...
pre purge is gonna be a minimum on that suggested lash up ....think about it for a cold sobering second.0 -
baromitric damper
this is a oil fired unit correct did they install a baromatric damper on the smoke pipe and does that fresh air boot on the burner air inlet have a baromatric relief on it maybe some put ascrew so it wouldn't make noise good luck maybe just take off the air boot qand run 6 in rd to a oval x rd ell and use 6 oval with a dual stack for combustion air more then one way to skin a cat p.s. that air shutter for the beckett gun can cause promblems in the future when they get jammed or restrict air to the burner there great for sooting up a boiler and a 12;00 clock at night cleaning just my 2 cents peaceR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0 -
the barometric on the combustion is a for sure good idea.
0 -
yes on the barometric
There is a barometric on the smoke pipe ,and a relief on the fresh air. There is such a good draw on the chimney it just pulls it though the easiest path right thru the fresh air piping (4" rnd), throught the air boot, the burner, the boiler, and up the hot air goes. Thanks for your input.0 -
The negative pull
Sounds like a very tall chimney.Riello did make a burner with a hydrolic air band to cover the squirrel cage.Great idea and cannot recall why it was eliminated.The only thing that I can see to reduce would be a properly sized chimney liner.Don't know if the chimney is oversized but reducing the diameter to the proper size may reduce loss..........marginally at best.
cheese0 -
Are there
any problems running this boiler?
Sounds like you have some extreme draft potential.
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Could be extreme draft
The chimney is over 40' tall and is inside the building envelope. The house sits up on a little hill with a constant breeze. The boiler lights off well, runs quitely, no soot. I'm going back next week with the draft guage.0 -
If possible
Could you get the combustion numbers as well as the draft?
Beginning with light-off, run cycle, and shut-down.
Thanks!
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I will get the numbers
The original problem, not yet solved, is what is percieved as excess cycling. This a fairly large house, 6300sq ft; 4 fan coil zones, 3 baseboard zones, a large radiant loop with tile warmers for 4 bathrooms,and a W/M 120 for domestic h/w. It's configured as a cold start. The boiler was origianlly packaged with a 1.45 nozzle, downfired once to 1.25, and then again to 1.10. On the coldest nights, 10 to 15 degrees, this thing has no problem keeping up and it still cycles. Before I did anything additional with controls I wanted to make sure all other mechanical issue were addressed. Thanks
0 -
i am thinking cold start...
maybe some speed drives on the fan coils blower motors ,and mixed returns ahead of a boiler bypass protection loop would help with the short cycling...maybe the outside air to the premix air is stuck open or is allowing too much outside air.0 -
outside air premix
The combustion air comes directly into the burner thru a Field Controls air boot that replaces the air band on the burner. It's all outside air going to the burner. Thanks for thinking.0 -
chimney
Its 8" sq masonry and at least 40' tall.0 -
if
the draft is too high going thru the unit add a second barometric damper.Looks goofy but works great.We had some Slant Fins that would draft to much and pull the flame up into the sections,just a thought,dave0 -
Barometric
I have seen several places with similar setups. They all had too high of a draft. A second barometric stopped that problem. Why the makeup air? Is it a tight area?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements