Outside Combustion Air

The boiler is a W/M with a Beckett AFG and Field Controls outside air kit on it. The chimney is masonry and at least 40' tall, with most of it inside the home. The question is -- There is a tremendous amount of air flowing thru the boiler when it is not running, there by increasing the standby loses. Any thoughts on how to control this? Thanks.

Comments

  • controlling combustion air

    Beckett makes an "inlet air shut-off" part #5861. This will stop any air from going through the burner.
  • Weezbo
    Weezbo Member Posts: 6,232
    careful there...

    pre purge is gonna be a minimum on that suggested lash up ....think about it for a cold sobering second.
  • clammy
    clammy Member Posts: 3,163
    baromitric damper

    this is a oil fired unit correct did they install a baromatric damper on the smoke pipe and does that fresh air boot on the burner air inlet have a baromatric relief on it maybe some put ascrew so it wouldn't make noise good luck maybe just take off the air boot qand run 6 in rd to a oval x rd ell and use 6 oval with a dual stack for combustion air more then one way to skin a cat p.s. that air shutter for the beckett gun can cause promblems in the future when they get jammed or restrict air to the burner there great for sooting up a boiler and a 12;00 clock at night cleaning just my 2 cents peace

    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating

  • Weezbo
    Weezbo Member Posts: 6,232
    the barometric on the combustion is a for sure good idea.

  • yes on the barometric

    There is a barometric on the smoke pipe ,and a relief on the fresh air. There is such a good draw on the chimney it just pulls it though the easiest path right thru the fresh air piping (4" rnd), throught the air boot, the burner, the boiler, and up the hot air goes. Thanks for your input.
  • Mike Kraft_2
    Mike Kraft_2 Member Posts: 398
    The negative pull

    Sounds like a very tall chimney.Riello did make a burner with a hydrolic air band to cover the squirrel cage.Great idea and cannot recall why it was eliminated.The only thing that I can see to reduce would be a properly sized chimney liner.Don't know if the chimney is oversized but reducing the diameter to the proper size may reduce loss..........marginally at best.

    cheese
  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    Are there


    any problems running this boiler?

    Sounds like you have some extreme draft potential.

    Mark H

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Could be extreme draft

    The chimney is over 40' tall and is inside the building envelope. The house sits up on a little hill with a constant breeze. The boiler lights off well, runs quitely, no soot. I'm going back next week with the draft guage.
  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    If possible


    Could you get the combustion numbers as well as the draft?

    Beginning with light-off, run cycle, and shut-down.

    Thanks!

    Mark H

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • I will get the numbers

    The original problem, not yet solved, is what is percieved as excess cycling. This a fairly large house, 6300sq ft; 4 fan coil zones, 3 baseboard zones, a large radiant loop with tile warmers for 4 bathrooms,and a W/M 120 for domestic h/w. It's configured as a cold start. The boiler was origianlly packaged with a 1.45 nozzle, downfired once to 1.25, and then again to 1.10. On the coldest nights, 10 to 15 degrees, this thing has no problem keeping up and it still cycles. Before I did anything additional with controls I wanted to make sure all other mechanical issue were addressed. Thanks
  • Weezbo
    Weezbo Member Posts: 6,232
    i am thinking cold start...

    maybe some speed drives on the fan coils blower motors ,and mixed returns ahead of a boiler bypass protection loop would help with the short cycling...maybe the outside air to the premix air is stuck open or is allowing too much outside air.
  • outside air premix

    The combustion air comes directly into the burner thru a Field Controls air boot that replaces the air band on the burner. It's all outside air going to the burner. Thanks for thinking.
  • chimney

    Its 8" sq masonry and at least 40' tall.
  • Dave Palmer_3
    Dave Palmer_3 Member Posts: 388
    if

    the draft is too high going thru the unit add a second barometric damper.Looks goofy but works great.We had some Slant Fins that would draft to much and pull the flame up into the sections,just a thought,dave
  • Maine Ken
    Maine Ken Member Posts: 531
    Barometric

    I have seen several places with similar setups. They all had too high of a draft. A second barometric stopped that problem. Why the makeup air? Is it a tight area?