water migration
Al_11
Member Posts: 34
I got a problem,
last fall I installed a Burnham Spirit boiler with a primary/ secondary set up. All was fine with the world until last week when I got the call that the boiler won't stop heating the house. I told the homeowner to shut the boiler off and I would be by this afternoon to check it out.
I start the system up cold and it hums right along, I have the t-stats off in both zones. Primary loop gets to temp (180) and cycles off. I feel the pipes at pumps and they remain cold. I shoot the bull for 20 min. and check again and I can feel the heat migrating through the pump just ever so slightly but it is happening.
I have got check valves on both returns, on the horizontal run to the primary. I have had a problem on other jobs where the water starts to backfeed through the return and the check's prevent this problem.
This is migrating through the pump, first time I have seen this. How can I stop it. HELP!
last fall I installed a Burnham Spirit boiler with a primary/ secondary set up. All was fine with the world until last week when I got the call that the boiler won't stop heating the house. I told the homeowner to shut the boiler off and I would be by this afternoon to check it out.
I start the system up cold and it hums right along, I have the t-stats off in both zones. Primary loop gets to temp (180) and cycles off. I feel the pipes at pumps and they remain cold. I shoot the bull for 20 min. and check again and I can feel the heat migrating through the pump just ever so slightly but it is happening.
I have got check valves on both returns, on the horizontal run to the primary. I have had a problem on other jobs where the water starts to backfeed through the return and the check's prevent this problem.
This is migrating through the pump, first time I have seen this. How can I stop it. HELP!
0
Comments
-
Are the pumps
located above the primary loop or below it? If they are higher, it might just be gravity flow up and down the same pipe.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
you could try a couple of IFC ....
circulators..what is you spacing of your tees? kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
another suggestion
If you find no problem's with the setup, I would consider looking into an underslung thermal trap..This should trap any flow you may have through the loop. I would first verify that the flow check is working and that there are no leak's in the loop itself. Also, out of interest, are your tee's as close together as possible as this will make a difference? good luck...:)0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements