Question about proper operating pressure
Options
Live/Learn
Member Posts: 97
I understand that the pressure for a hot water system should be set @ 12-15lbs. My question is is the pressure set with the boiler cold or at the high set point? My pressure shows about 15lbs @ 110 degrees but at 180-190 lbs goes up to about 23-24lbs. My extrol#30 is set for 12lbs with pressure released from the boiler. pressure drops back to 15lbs when boiler temp drops back to 110degrees.Is this normal? Thanks in advance, RE Hoyt
0
Comments
-
in a nut shell...sound's like your all set...generally a system is set to 12lb's cold..when they heat to operating temp they rise to app. 22lb's...unless you have problem's with the pressure relief valve spilling I wouldn't be overly concerned..:)0 -
i agree
0 -
system pressure
Thanks Guys for the quick responce and releaving my worries. RE HOYT0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements