I understand that the pressure for a hot water system should be set @ 12-15lbs. My question is is the pressure set with the boiler cold or at the high set point? My pressure shows about 15lbs @ 110 degrees but at 180-190 lbs goes up to about 23-24lbs. My extrol#30 is set for 12lbs with pressure released from the boiler. pressure drops back to 15lbs when boiler temp drops back to 110degrees.Is this normal? Thanks in advance, RE Hoyt

Comments

  • lchmb
    lchmb Member Posts: 2,997
    Options


    in a nut shell...sound's like your all set...generally a system is set to 12lb's cold..when they heat to operating temp they rise to app. 22lb's...unless you have problem's with the pressure relief valve spilling I wouldn't be overly concerned..:)
  • Weezbo
    Weezbo Member Posts: 6,232
    Options
    i agree

  • Live/Learn
    Live/Learn Member Posts: 97
    Options
    system pressure

    Thanks Guys for the quick responce and releaving my worries. RE HOYT