Load Calc for a basement
Brian V
Member Posts: 7
Hey all,
I'm finishing my basement, making a playroom for the crumb snatchers. I ran a load calc on it (heating only), finding it a bit hard to believe the btu's needed (12-14,000). I ran it in both Wrightsoft and Hydronic Explorer, thats why the difference in btu's. If someone can double check for me and make sure I'm not screwing it up. I can see the load if the area was all above grade experiencing the 0deg. Even with no heat the basement maintains 53-55deg...just can't agree with the 12-14mbtu.
Room:
4.5 feet below grade 3feet above grade.
0 degree (Worcester, MA)
70 degree design temp
14x28 feet, 7.5' ceilings
8" concrete
2x4 framing w/R13 bats
Cold partition is 64'
remaining 28' is the other half of the basement, unheated.
1 window double pane, low e 21x31"
1 door, steel, foam fill, 78x36", under a bulkhead (treated as w/storm).
Under finished/heated living space. R19 bats.
Hydronic baseboard.
Boiler design is 145deg (I'm using a proportional controller, high 180 low 145).
Thanks all,
-Brian
I'm finishing my basement, making a playroom for the crumb snatchers. I ran a load calc on it (heating only), finding it a bit hard to believe the btu's needed (12-14,000). I ran it in both Wrightsoft and Hydronic Explorer, thats why the difference in btu's. If someone can double check for me and make sure I'm not screwing it up. I can see the load if the area was all above grade experiencing the 0deg. Even with no heat the basement maintains 53-55deg...just can't agree with the 12-14mbtu.
Room:
4.5 feet below grade 3feet above grade.
0 degree (Worcester, MA)
70 degree design temp
14x28 feet, 7.5' ceilings
8" concrete
2x4 framing w/R13 bats
Cold partition is 64'
remaining 28' is the other half of the basement, unheated.
1 window double pane, low e 21x31"
1 door, steel, foam fill, 78x36", under a bulkhead (treated as w/storm).
Under finished/heated living space. R19 bats.
Hydronic baseboard.
Boiler design is 145deg (I'm using a proportional controller, high 180 low 145).
Thanks all,
-Brian
0
Comments
-
I come up with
14.2 btu/ square foot for 392 square feet (14X28), with no under slab insulation, no exterior foam insulation?
The HDS software has a basement calculator that works real nice for this example. www.hydronicpros.com
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
BTUH Needed
Using a quick thumb rule for ball park estimation multiply the square feet of the space by 30 BTU's per sqft. and divide by 2.
The # 2 is the constant that adjusts for the windows, doors
and the above ground aection of the basement.
14 X 30 = 11760 BTYU's divided by 2 = 5880 BTUH.
In all actuality you would about 4800 BTUH becuase the constant temperature is in the 50+ degree range.
Jake
0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements