Taco 110 circulator

Options
joe_6
joe_6 Member Posts: 23
Can the 110 circ.be mounted horizontal or just vertical.Thanks

Comments

  • Mark Eatherton1
    Mark Eatherton1 Member Posts: 2,542
    Options
    You can mount it any direction you want...

    so long as the motor shaft is parallel with the gorund, and the oil cup on the bearing assembly is pointing up:-)

    You can accomplish this by pulling the four bolts that hold the B/A onto the volute and turning it so the oil port is pointed up.

    ME

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Joe Mattiello
    Joe Mattiello Member Posts: 707
    Options
    110 circulator installation instructions

    Good morning
    Thank you for using Taco products. Attached is the installation instruction sheet for the 100 series circulators. The correct mounting orientation is the motor shaft parallel to the floor. However, the flow direction can be horizontal, or vertical, the pump doesn't care. You can index the casing 90 degrees to meet your system requirement. The motor must be horizontal to keep the lube oil from weeping out the oil fill ports located at the top of the motor. Taco, does offer vertical pumps including multistage types. Please visit www.taco-hvac.com for a complete list of all products.



    Joe Mattiello
    Technical Support Services
    Tel. 401-942-8000 X 484
    Fax. 401-942-2360
    joemat@taco-hvac.com

    Joe Mattiello
    N. E. Regional Manger, Commercial Products
    Taco Comfort Solutions
  • Billy_3
    Billy_3 Member Posts: 42
    Options
    taco 110

    When is it neccassary to use a 110. I have never used one.
  • Steamhead
    Steamhead Member Posts: 16,861
    Options
    The 110

    is a very popular unit- it has a similar capacity to the B&G 100 circulator.

    It is best suited to jobs that don't have a lot of head (back-pressure) since it can only pump up to 10 feet or so. It has a capacity of about 30 GPM at a 3.5 foot head, which makes it a good choice for converting larger gravity systems of 900-1200 square feet EDR or so to forced circulation (see

    http://www.heatinghelp.com/newsletter.cfm?Id=125

    for more on this).

    As long as it's properly lubricated, the 110 will last a long time. I see many older units out there, still pumping. And it's backed by people like Joe Matiello, who hang out on the Wall!

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"