New Riello burner w/ buderus G115: anyone else issues?
Stew_3
Member Posts: 2
Since Riello changed their blast tube design less than a year ago, has anyone else had issues with proper setup and stability? Is it just the match up with the Buderus G115 series?
0
Comments
-
BF Burner
Only with the BF series burner . The Buderus blue F series is plug & play...0 -
What is the difference in the applications of one versus the other? We do residential retrofits for baseboard applications with indirects mostly; not very much radiant.0 -
BF
The BF(balanced flue) has a fresh air intake piped to the outside .It is used with a direct vent set up. Instead of a chimney , the boiler is vented ,without electrical power through a outside wall.. You can also use it without the direct vent.Reasons efficacy ,noise,lint area , ect.... You need to use the post purge BF model for a direct vent....0 -
did you try to.....
call Buderus? I am told that a former riello rep.guy is now working FOR Buderus...might have a pretty good idea about how to fix it....kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Charlie Smith is with Buderus,
> call Buderus? I am told that a former riello
> rep.guy is now working FOR Buderus...might have a
> pretty good idea about how to fix it....kpc
>
> _A
> HREF="http://www.heatinghelp.com/getListed.cfm?id=
> 323&Step=30"_To Learn More About This
> Professional, Click Here to Visit Their Ad in
> "Find A Professional"_/A_
0 -
Buderus Rep
Charlie Smith, was with Riello, now with Buderus, but any one @ Buderus technical could help you out.0 -
BF series problems
Yes - there have been numerous cases with issues
Very touchy to settings and don't light off well (strong pulsations, sooty smells, occasional retries on start)
Had one installed late last year and it took a lot of tweaking to get it working and to date it's still not quite right.
Big Ed had suggested a few things that seemed to really help significantly. Boost pump pressure to same spec as F series (170-180 psi) and start with turbulator and air setting for F series, and work from there.
Best thing for all is to keep lots of pressure on Riello and Buderus because they need to get their hands around this issue.0 -
I've installed
the BF's in laundry room/boiler rooms.Vented the appliance in a chimney.Avoiding bad makeup air conditions.I like to avoid the direct vents like the plague.Paranoid........me?,yup
cheese
0 -
Started a thread on this at Oil Tech Talk
http://disc.server.com/Indices/24736.html
Make sure you check out the Riello response to Eleft's warranty question!!
Definitely agree, talk to Buderus. Riello has not been helpful on this isssue with me.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements