Primary/Secondary Parallel sizing?
Steve_45
Member Posts: 39
If Im setting up a primary/secondary boiler with 4 circulators in Parallel loops and the primary is 1 1/4 can the parallel pipes be 3/4 or do they also have to be 1 1/4? The total primary loop will be approx. 20 feet total and the secondarys are 151, 130, 110, 98 feet respectively. Each with its own taco 007. Primary will also
have a Taco 007.
||---TT---|| || = 1 1/4
||---TT---||
||---TT---|| ---- = 3/4 ??????
||---TT---||
Thanks,
Steve
have a Taco 007.
||---TT---|| || = 1 1/4
||---TT---||
||---TT---|| ---- = 3/4 ??????
||---TT---||
Thanks,
Steve
0
Comments
-
Flow
Someone correct me if I'm wrong, but it should be based on your heatloss calc for that zone. BTU load/500XdeltaT. 500 is for water. 10,000 BTU load with a 20 degree delta T= 1GPM. Then you would find a pipe size that would move that much water at the proper velocity. I have a table for it at home, but I'm sure someone may be able to send you a link that would help you out. As far as I know, this would be the "correct" way to do it.0 -
Thanks Dave,
Larges BTU loss is 30000 other three are around
20000 each. That table sure would be helpful.
0 -
Pipe size
OK- according to my table, 3/4" would be fine for all secondary zones that you have listed. 3/4" would be alright up to 4 GPM. Hope this helps.0 -
Thanks again Dave,
According to the formula you gave everything
looks good also.
Thanks for your help,
Steve0 -
Primary/secondary, Taco, circulators
Good Morning
Primary, secondary piping is an excellent versatile piping technique used for multizones/multitemperature systems. Primary circulator is sized by the design temperature differential. Assuming a 20 degree delta, 150,000btu output, formula is 150,000/500x20=15gpm. The piping is sized to accommodate the flow rate without exceeding 4'per second velocity. Taco, 007-F5 will work just fine. The use of closely spaced tees to minimize the potential for induced flow in the secondary circuits is fundamental. Secondary piping tees have to be placed no more than Four times the nominal diameter of the primary loop piping apart. The secondary pipe size is dictated by the flow rate required for each loop, which is based on the load calculated in each circuit.
Joe Mattiello
Technical Support Services
Tel. 401-942-8000 X 484
Fax. 401-942-2360
joemat@taco-hvac.com
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
Joe 007-F5? All mine just say 007-IFC0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements