Check valve ?'s

Options
Jack_23
Jack_23 Member Posts: 153
What are you using on your heat systems for check valves. Swings or springs? Why do you like one or the other. Is one better than another for certain systems (heat/potable)? I've had some issues and would like your thoughts. TIA!

Comments

  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    Options
    have pretty given up...

    on check by themselves. I now almost only use the grundfos ifc or an occational taco ifc. I still use an occational swet check. Spring checks would work fine for a bit but I wonder about their longevity. kpc

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Check Valves

    Spring check valves are used on the discharge line of pumps that cycle on and off. The spring in the check valve helps prevent the Check (flap) from banging against the seat of the check valve every time the pump cycles on.

    Swing check valves are used to keep a fluid flowing in one direction. The swing check valve works best when used on a constant flow system or where back pressure is not generated quickly.


    Jake
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,531
    Options
    Just curious

    Why do you prefer the Grundfos over the Taco IFC, Kevin?
    Retired and loving it.
  • Kal Row
    Kal Row Member Posts: 1,520
    Options
    also

    the Grundfos ckv is on the discharge side where it can not affect the NetPositiveSuctionHead (cavtation protection) and is serviceable - i had one chatter recently because of dirt - it was real easy to clean up

    spring checks are important to protect against convective heat migration - ie - cooler water being more dense drops like a rock and displaces warmer water even in a single pipe, so if your zone valves are on the return side, and as a result the zone supplies, are open to the hot supply header, -you need a spring check on each, or all the heat, will just migrate up the 'effectively" open zones to the highest point
    same goes for a indirect domestic hot water tank – even the warm water from return header is still cooler than the standing water in the coils of the IDHW tank, and will drop right into the coils of the IDHW tank without a spring check

    so use spring checks to guarantee flow only when you want it – make sure they are serviceable, and try to cut down the amount of them, by piping downward from hot to cold by at least 18 inches where possible – eg having zone valves on the supply and even then – take them off underneath the supply header, for pri/sec/injection, inject downward from the boiler loop to the bottom of the system loop just past the returns, pump the IDHW coils in hot at the bottom and return at the top then down to the boiler’s return

    little tricks like those heat trap loops that can save a lot of spring checks and be less restrictive to the pump than the spring check
  • Rocky
    Rocky Member Posts: 121
    Options
    What brand of spring checks for heat?

    Have several applications where we use the spring checks. Would use the IFC pumps, but the only one we get up here in Fairbanks is the Taco 007. Have lots of applications where I need a 0010, or 0011 etc so have to resort to spring checks. What brand do you guys use. It is like pulling teeth here to get something other than those rated for cold water well lines. Unrelated issue, suppossed to go to -25 tonight here. Who says spring has sprung?
    warm regards from chilly Fairbanks,
    Rocky
  • John White
    John White Member Posts: 120
    Options
    input

    There is great input here for us a Taco. Thank you all.
    The ifc is available in the 0010 and 0011, as well as all the rest of the Taco circ models. I will make certain someone gets in touch with you as to where you can find them....even in Fairbanks!
    The location of the ifc is a constant source of debate, and we are looking at that.
    Again, thanks for the input.
    jhw
  • Kal Row
    Kal Row Member Posts: 1,520
    Options
    when are your 00VV pumps shipping?

    heatTimer makes a vraiable voltage control compatible with it
  • Joe Mattiello
    Joe Mattiello Member Posts: 707
    Options
    Integral, or external checkvalves

    Good Afternoon
    Thank you, for using Taco, products. Check valves, are always recommended when zoning with circulators, to prevent migration. In some cases they are used on the supply, and return, if the pressure drop is too high with primary, secondary piping. This adds additional resistance, and cost to the system. Taco, introduced a circulator line with integral flow checks, 00 series ifc (integral flow check), that is well recognized in the HVAC industry as being a quality product, at a relatively, low cost. The IFC circulators are available in several sizes, including the 0010, and 0011s, giving you more capacity, and an increase in performance. Additionally, the check valve is replaceable should it fail, but if it's a Taco pump you may never have to replace it. For your convenience I have attached the submittal data sheets for the Taco 0010-F3-IFC, and the standard 0010-F3 to compare performance characteristics. Please advise, if you require additional assistance.
    Joe Mattiello
    Technical Support Services
    Tel. 401-942-8000 X 484
    Fax. 401-942-2360
    joemat@taco-hvac.com
    Joe Mattiello
    N. E. Regional Manger, Commercial Products
    Taco Comfort Solutions
  • hr
    hr Member Posts: 6,106
    Options
    The 15-58 Grundfos

    is a 3 speed pump so it covers a lot more range than a single speed. Check is in the discharge, and it has a 3 year warranty. What's not to like :)

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Steve_45
    Steve_45 Member Posts: 39
    Options
    P/S

    Kal could you please explain this in a little more
    detail. "to the bottom of the system loop just past the returns" a diagram would help if possible. Nothing fancy.
    Thanks,
    Steve
  • Kal Row
    Kal Row Member Posts: 1,520
    Options
    attached is a diag

    in this instance - i had to pipe the takoffs upward because there was other pipes below the system loop so the returns had to come in downward, as a result, forcing the zone supplies to come off the top, but it's not a problem here because a closed ZV stops the convection on the supply, and ther shouldnt be too much convetion on the open returns with it being on the bottom of the system
  • Kal Row
    Kal Row Member Posts: 1,520
    Options
    tekmar doesnt support less than speed #2

    on their injection controlers with this pump because of the low starting torque - but a VV pump is desinged to start with full torque even at the lowest setting - doesnt mean that grundfoss cant make it, in fact the do on the magna series - they just havent made it for the USA market yet
  • hr
    hr Member Posts: 6,106
    Options
    Kal

    I'm not sure you would use a 3 sped pump for injection. The Grundfos 15-42 would be a better choice. The 15-58 on speed 2 is very similar.

    The VV pump is DC? How else would it start with full torque? I'm sure you remember the UFC VS pump. Talk about starting torque.

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    Options
    well a few...

    reasons. 1)The location of the check valve on the outlet.
    2) the 3 speed option 3) the wire terminals 4)and the boxes for wiring seem to be attached to the pump housing better...kpc

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Kal Row
    Kal Row Member Posts: 1,520
    Options
    doubt that it's DC

    brushless DC make a lot of noise unless they have active circuitry like you hard disk has – too expensive – and switched reluctance would be even more expensive, nah, it’s probably a duty cycle waveform chopper like other controllers, just that it is signaled by input voltage, but being that it’s integral with the pump, it can get feedback and provide full torque until it reaches desired speed
  • Kal Row
    Kal Row Member Posts: 1,520
    Options
    ps according to tekmar

    even on speed 2 you want to stop down balance valve a bit to give to something to push against, it seems, for longevity of the pump, you want the mixer to run at 60% or higher

    ps - i picked up a whole lot of 15-58fc's real cheap, so i used it, probably got it, because they were trying to get rid of old stock, for the cosmetically changed superbrute II label,
    also with the manufacturing move to the USA from Germany it got a lot cheaper for them
  • Jimmy Gillies
    Jimmy Gillies Member Posts: 250
    Options
    Checkvalve.

    That's a very cool product Joe. I don't think anything like that is available in the UK. Who says Europe is ahead of the US with HVAC products ?
    Kind regards.
    Jimmy Gillies.