Low ambient A/C maintainance?
Alan_6
Member Posts: 87
Is the a way to do a accurate check of refrigerant charge, in low ambient conditions on a residental split A/C system? Some people think you can by restricting the air flow across the condensor. I have had no luck with this method.
0
Comments
-
charging
chk your sub cooling on your liquid line and also chk your super heat at your suction line near your condensing unit.Is this for a/c or refrigeration and what type of low ambeant control are you using a fan cycler or a fan speed controller there's a couple of varables.Also chk the manafactors spec they usally tell all restriction air across the condenser is a load of bs it's not the way to do itR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0 -
I also think loading up the condensor is bs. I was just looking for opinions. The people that dispatch our calls send us out to check the charge on residential split systems. When it is as cold as 40 degree's outside. It never works, as a result, lots of call backs.0 -
charging
use a P/T chart.
take your ambient reading add 30degrees and croos check your
suction reading.
not the best method but effective and very close until you get back some warm day...like that will happen.
we have done some Nextel sites in the winter and have to charge the system it works.
steve0 -
loading
By the way loading up the condenser is a very bad idea.
liquid slugging will kill the compressor if it is loaded to much and it backs up in the condenser which diminishes it's ability to reject heat.
steve
0 -
What we do
is try to check residential a/c's starting in May. Even then some mornings can be around 40 degrees. We check the temperature difference on the indoor coil. If it is between 15-25 degrees then all is good. The reading is also recorded on the job order. This is not perfect but there are very few callbacks. I am not a fan of checking system pressures as part of maintenance. Servicemen loose the caps, the cap gaskets fall out, or just don't put them back on. Then you have a leak. Unless you have a charging chart by the manufacturer for that particular unit most people cannot get the charge right. JMHO
David0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements