oil

jake b
jake b Member Posts: 1
after i receive a oil delivery my bock oil fired hot water heater with a riello m3 burner will not fire until i hit the reset. I have no problem till the next delivery.i have one filter feeding my boiler and hot water heater. its a 2pipe system fed out of the top of my oil tank.any suggestions thanks

Comments

  • Firedragon_4
    Firedragon_4 Member Posts: 1,436
    Have them split the line and add

    a filter for each one!
  • maine rick
    maine rick Member Posts: 107


    happen to us our oil trucks pump to fast and it was making air bubbles talked to the drivers and told them not to kick up into high rpm on there pto's. solved the problem
  • john_35
    john_35 Member Posts: 29


    have them split the lines IF both supply and return go all the way to within 3" of the bottom of the tank. If the return terminates at the top of the tank you can't use it for a supply. Is the tank in the basement or buried? This is a situation where you need to cut the flow rate. Having a single line feed will do that but if there's significant lift (more than 8 vert feet) you probably want to use a "Tiger Loop". (Do you think they'll pay me a stipend for hawking their product all over this site?)Anyway, it's always best not to filter more oil than you are actually consuming. Two line systems pump way too much oil thru the filter(s) and cause customers to dread their deliveries.
This discussion has been closed.