American Standard boiler input?

G Averill_2
G Averill_2 Member Posts: 48
Would anyone have the catalogued gas input on American Standard 4G-11 series boilers? One of our contractors hasa job to replace two of them promptly in a nursing home in southeast Nebraska, where the rating plates have been removed. My library data does not include the -11. Any help would be appreciated.

Comments

  • Steamhead
    Steamhead Member Posts: 17,387
    In the Hydronic Rating Handbook

    the 4-G-11 is rated as follows:

    Input- 1200 MBH

    Net Steam- 2935 square feet/704.4 MBH

    Net Hot Water- 4690 square feet/703.9 MBH

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Bill Nye
    Bill Nye Member Posts: 221
    How do

    How do you know the previous contractor installed the right sized boiler? You know what happens when you ****-u-me!

    Maybe your contractor could do a heat loss or at least an installed radiation survey?
  • bob young
    bob young Member Posts: 2,177
    good point

    we never go by the existing rating plate. there are just too many cowboys out there with that one size fits all mentality
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    And besides it may be against code...

    The more recent codes prohibit the replacement of heating equipment without conducting and following a proper heat loss calculation.

    Boilerpro
  • G Averill_2
    G Averill_2 Member Posts: 48
    Heat Loss

    I calculated the actual heat loss of the building(s)at 1101mbtu. The request for the input of the existing
    product(s)was due to questions by the contractor that had to do with venting and gas pipe sizes. We decided that we will be replacing these two with three 399M Munchkins.
    Thanks for your replies and concerns.