Pressuretrol Settings-Residential

K. Corbett
K. Corbett Member Posts: 1
What is the ideal setting of the pressuretrol in a 2 story house?

Comments

  • ed wallace
    ed wallace Member Posts: 1,613
    pressueretrol setting

    as low as possible on the wheel under the cover set at 1 psi on the scale on the face of unit set at 1/2 psi

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Pressuretrol settings

    Steam pressure settings in any building has nothing to do with the height of the building.

    Steam pressure is set based on the pressure drop of the piping system. The pressure drop in a piping system is based on the frictional resistance of the piping.

    Because I donot know the pressure drop of the piping system you can start at setting the pressuretrol at 1 1/2 PSI with a 1/2 lb differential and work your way down to 1 PSI set pressure.

    Make sure that all your vent valves are operating properly or if you have steam traps in the system make sure your master vent works and that your steam traps are working properly.


    Jake