Pressuretrol Settings-Residential
K. Corbett
Member Posts: 1
What is the ideal setting of the pressuretrol in a 2 story house?
0
Comments
-
pressueretrol setting
as low as possible on the wheel under the cover set at 1 psi on the scale on the face of unit set at 1/2 psi
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Pressuretrol settings
Steam pressure settings in any building has nothing to do with the height of the building.
Steam pressure is set based on the pressure drop of the piping system. The pressure drop in a piping system is based on the frictional resistance of the piping.
Because I donot know the pressure drop of the piping system you can start at setting the pressuretrol at 1 1/2 PSI with a 1/2 lb differential and work your way down to 1 PSI set pressure.
Make sure that all your vent valves are operating properly or if you have steam traps in the system make sure your master vent works and that your steam traps are working properly.
Jake
0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements