3\" Stainless Steel Venting

Cory_2
Cory_2 Member Posts: 10
We have a large inventory of 3" stainless steel FasNseal Gasketed venting that we are no longer in need of because we now install Viessmann boilers. If anyone is interested in purchasing any venting, everything we are selling is in the box and has never been opened. We will only be selling venting in box quantities, if anyone is interested please call or email me, we hate to waste or throw away any or all of this new product.
Cory
(509) 747-0950
Cory@moserheat.com

Comments

  • kf_2
    kf_2 Member Posts: 118
    3\" SS Venting

    Cory,

    You may want to hang on to that 3" venting. The Vitodens boilers are now approved to be vented with single wall stainless vertically.

    The WB2 6-24C & 6-24 can be vented vertically up to 66' with 3" stainless and the WB2 8-32 can be vented up to 49' with 3".

    The larger ones use 4" stainless.(WB2 11-44 & 15-60)

    This is for applications with no outside wall.

    REMEMBER to bring combustion air into the mechanical room as you will not be using the standard concentric kit in these applications.


    kf