Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Calling Jeff Cook
Jack Smith
Member Posts: 53
I was wondering if you were experience any minor problems with the Vision 1. I have an install where the boiler shuts down and won't fire again until the outdoor sensor is disconnected. No fault code is being displayed. It has run for up to two weeks at a time with no problem. I realize that most problems associated with the Munchkin are created by the mis-installation. Any insight or tips would be greatly appreciated!
0
Comments
-
I'm not Mr. Cook,
but, had one doing this, what was happening was that the thermistor was mis calibrated and the boiler was shutting down on WWSD. New sensor, no more problem. In the back of the vision one manual are the resistance charts for the thermistors.
J0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements