hot water heater problem
j tatum
j tatum Member Posts: 1
Im working on a hot water heater with a circulation pump the house is 3800sqft ranch home one end of the house does not have hot water at the sinks or showers instantly what might be the problem ohter than air in the system
  • Robert O'Connor_7
    Robert O'Connor_7 Member Posts: 688
    PUMP??
    Are you sure the pump works??
  • Ray Landry
    Ray Landry Member Posts: 203
    Air wouldn't have anything to do with your problem. Domestic water is an open loop system. You probably have a bad re-circ pump, or maybe a check vavle thats stuck open. sounds like you need to call pro. Use the 'find a professional' link to your left
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,012
    split loop
    Hello: In such a big house you may have a split recirc loop... basically two or more loops driven by one pump. If they are not balanced, you'll get most of the flow through one loop. A restriction where the recirc pipe comes back into the heater is another possibility. That connection tends to plug up from the action of the anode in the tank. Try running water under pressure through the various parts of the system. You'll either find very dirty water indicating poor pumped flow or just very little flow when flushing, telling you there is a restriction. Good luck!
  • Big Ed
    Big Ed Member Posts: 1,117
    Aquastat
    First try a easy fix..On the return for the recirculation system there should be a aquastat .This control starts and stops the recirculation pump which charges the hot water lines . If the return pipe cools down it would turn on the pump , pulling hot water up the hot water supply and back to the heater. Try raising the control up a tad , maybe it's too low......