diverter tee problem
Options
[Deleted User]
Posts: 55
i recently had to cap off a radiator on this system.. this system circles the basement of the house with diverter tee's for the radiators.. i capped the two lines in the basement, bled the radiators and everything is working fine, except they called me to tell me they heard the water flowing through the pipes a little loud through the house.. the temp is at 160 and the pressure is at 10 lbs... any help? thanks
0
Comments
-
diverter tee problem
Is you want to eliminate the noise, remove the caps and run a parallel pipe between the tees or remove the tees.0 -
As UniR said
NEVER "cap" lines in a diverter Tee system. If you have to disconnect a convector, you sholud put a cross-over pipe between the two tees.
Try it, you'll like it!!!!!!!!
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements