Mark E
Options
Billy_3
Member Posts: 42
Date: February 17, 2004 10:47 PM
Author: Mark Eatherton (athotmaildotcom)
Subject: What...
is the configuration of the series string. How many feet of BBR, where. I.E. Boiler, 10 feet 1/2" PEX, 7 feet BBR with 300 BTUH load, 10 feet PEX, 15 feet BBR, 7500 BTUH load and so on and so forth. I can use Siggys Wonderful Software to tell you what will happen, but need a lot of data on your part, including room loads in BTUH.
ME
--------------------------------------------------------------------------------
Date: February 18, 2004 08:02 AM
Author: Frank (Frank)
from the boiler there would be about 30 feet of pex. Then 13 feet of slant fin 30 7,107 btu. Then about 8 feet 1/2" pex feeding 15' of slant fin 30 8800 BTU. Then 8 feet 1/2" pex feeding 11 ' slant fin 80 7600 BTU. Then 20' of 1/2" pex feeding 4' slant fin 80 2500 btu. 8' 1/2" pex feeding 5' slant fin 30 and then 30'1/2" pex back to boiler.
Author: Mark Eatherton (athotmaildotcom)
Subject: What...
is the configuration of the series string. How many feet of BBR, where. I.E. Boiler, 10 feet 1/2" PEX, 7 feet BBR with 300 BTUH load, 10 feet PEX, 15 feet BBR, 7500 BTUH load and so on and so forth. I can use Siggys Wonderful Software to tell you what will happen, but need a lot of data on your part, including room loads in BTUH.
ME
--------------------------------------------------------------------------------
Date: February 18, 2004 08:02 AM
Author: Frank (Frank)
from the boiler there would be about 30 feet of pex. Then 13 feet of slant fin 30 7,107 btu. Then about 8 feet 1/2" pex feeding 15' of slant fin 30 8800 BTU. Then 8 feet 1/2" pex feeding 11 ' slant fin 80 7600 BTU. Then 20' of 1/2" pex feeding 4' slant fin 80 2500 btu. 8' 1/2" pex feeding 5' slant fin 30 and then 30'1/2" pex back to boiler.
0
Comments
-
Frank.
The 1/2 inch PEX will work. However, your baseboard lengths in the order you gave them to me are 15 ft, 20 ft, 16 ft and 6 feet. I assumed neglible pressure drop through the boiler, and a Grundfos 1542 on speed 2 is just about perfect.
You are on the jagged edge of velocity at 4.1 feet per second.
It should work just fine.
ME
0 -
thank you
Thank you very much I really appreciate the help0 -
You're welcome...
the increase in baseboard lengths is due to the decreasing fluid temperature as it flows through the series circuit.
As a possible alternative, you could consider using a four port manifold, and then all 4 BBR's would see the same entering water temperature, and the amount of board could be lowered. PEX is cheap.
ME0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements