pex heat lines

Billy_3
Billy_3 Member Posts: 42
I just wanted to know if you guys think there is anything wrong with running 1/2" pex for heat lines on a new baseboard loop. I have always run 3/4 copper and I have talked to a lot of other plumbers and a lot of them think I am crazy.

Comments

  • Al_3
    Al_3 Member Posts: 79
    Pex heat lines

    No prob with that at all, granted that you have done the flow calcs for your particular application.
  • Billy_3
    Billy_3 Member Posts: 42
    I have

    But is there any reason that copper would be better? I don't know why but for some reason I just like running copper better. If it is not neccesary then I am wasting my time I guess
  • Mike Kraft_2
    Mike Kraft_2 Member Posts: 398
    You might try.........

    pex - aluma-pex.I use Wirsbo's multi-core tube.You can run a feed and return from manifolds to all your baseboard and have a very even temp.Very nice.

    cheese
  • Keith_5
    Keith_5 Member Posts: 24
    pex lines

    Frank, We just finished an affordable housing project using pex for the branch piping. We piped it in a reverse return arrangement(copper), zone valves off the mains with isolation ball valves and purge valves. The branches were all 5/8" pex to the baseboard. Worked like a champ and saved a ton of labor.
    Be a little careful with the 1/2" in regards to your btu capacity.
    Good Luck, Keith
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    keep the runs to baseboard

    loops less than 30' of fin... it gets a bit iffy after that if you want to keep that 20F delta T. You could go w/ a split loop and stretch it more.kpc

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • hr
    hr Member Posts: 6,106
    5/8\" is

    often used for baseboard runs. all the manufactures have a 3/4" sweat to 5/8 pex ells.

    I, too, like pex al pex for baseboard runs. In addition to less expansion, and ease of installation, it is easier on the element, strain wise.

    More flow than 1/2" but you still need to run some cals for btu carrying capacity.

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • heatboy
    heatboy Member Posts: 1,468
    I agree, Cheese.

    Setting a manifold and running individualsupply and returns to each room or area, is the only way I do baseboard, convectors, radiators, etc. Wirsbo MultiCor really works well with this. Each room gets the same water temperature so calculating drops is not needed. Also, less electrical consumption from the pump. For the most part. I can set my Grundfos 15-58 on speed one and still get less than a 20° drop across the baseboard with 40 watts of power. Zoning is also super easy with telestats mounted to a central manifold station(s)or non-electric valves on the units. With all of the better piping options available, series piping should become obsolete.

    hb

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"