Bad Radiator Valve?
Tom_42
Member Posts: 63
One pipe steam system, just serviced. After about an hour and all the radiators are pretty hot there is one radiator that started hissing, not from the vent, from the valve. I tried to turn the valve off and it did not work. Looks like it is possible broken. So I tried tightening the top of the valve and that seemed to slow down the escaping steam. Then I decided to take the vent off and see what happens. Bad idea. Tons of steam started screaming out of the vent. I suppose I was really lucky in not getting scalded. Anyway I turned off the boiler and it took a few minutes for the steam to leave the pipes. This makes me nervous. Should there be that much pressure in the pipes? Shouldn't the boiler shut down at say 5 PSI? Makes me nervous.
0
Comments
-
hissing
Tom, normal operating pressure for a residnetial system is 1/2lb to 1 1/2 lbs. 5 PSI is way too much. It sounds like the stem packing is bad on your radiator valve. Call in a good steam guy to correctly set the pressure (and probably put on a new gauge, and repair the valve. It's not worth getting hurt over what the job will cost. And the education will be worth every penny.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
Thanks Al
I have someone coming on Saturday. I got his name from this site. Anyway, I think my burner might be overfired. It is rated at 1.25 gph to put out 420 sq ft of steam. By my calculations the load is only 330 sq ft of steam and the fire rate was set to 1.5 gph. What should I do?0 -
Wait for the pro to come over
good luck Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
Thanks
Mad Dog. Should I call back my service provider and have them change the fire rate back? I am not sure if the steam expert would want to do that. I am on a contract with a service provider. What do you think?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements