Copper Pipe in old 2-Pipe System?
Cecil
Member Posts: 3
I have a 1929 2-pipe steam system with a new boiler. All works fine. While renovating my bathroom, my contractor damaged a piece of old pipe (I assume cast iron) and replaced a segment with copper. Will the mixture of the two types of pipe damage the system?
Thanks
Thanks
0
Comments
-
Is this
a steam or return pipe?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
It is a steam pipe. Not a return.0 -
Replace it
with black steel. Those soldered joints will leak in a few years, as they can't "give" when the pipe expands and contracts.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements