Initial settings for L8124 Aquastat

Ken_13
Ken_13 Member Posts: 23
I posted here awhile back and got great info on splitting out my boiler ignition from the triple aquastat. In the new configuration I have an L8124 aquastat and it seems liek the boiler is firing way too often. That said, the current settings are HI=180, LO=140, DIFF=15. What ar ethe recommended settings? Burnham Oil Burner for a furnace heating a decent size house heating 12 rooms on 2 floors, all one zone. If location makes a difference, I'm in the Philly area.

Thaks for help in the past and in advance regarind this thread!

Ken

Comments

  • Ken_13
    Ken_13 Member Posts: 23
    Settings for L8124 Aquastat

    I posted here awhile back and got great info on splitting out my boiler ignition from the triple aquastat. In the new configuration I have an L8124 aquastat and it seems like the boiler is firing way too often. That said, the current settings are HI=180, LO=140, DIFF=15. What are the recommended settings?

    Burnham Oil Burner for a furnace heating a decent size house heating 12 rooms with radiators on 2 floors, all one zone. If location makes a difference, I'm in the Philly area.

    Thanks for help in the past and in advance regarding this thread!

    Ken
  • Al Letellier
    Al Letellier Member Posts: 781
    aquastat settings

    Usually, we set the hi/low 20* apart with the diff. @ 20.
    You didn't mention domestic but I assume you have a coil??
    The settings depend on the system and the demands put on it by design temps. You said firing too often: Is the boiler undersized or borderline? This can cause repeated on/off cycling or if it's too big, it will have a shorter run cycle. Check the connected load and adjust accordingly.
    We always set 20* spread with a coil, wider if a demand start and you're looking to protect the boiler from condensation or thermal shock. In that case, set the high at design and the low at manuf. recommended low setting.
  • Ken_16
    Ken_16 Member Posts: 1


    It is a domestic application.

    I'm not sure if the boiler is undersized or borderline. It's a V-15A-T

    How do I tell if it has a coil?

    Note: I'm just a homeowner....
  • jon_6
    jon_6 Member Posts: 26
    8124

    generally what i have have done as a oilburner tech is set the high at 180 and the low at 160 and diff at 10, if you have a coil (which is were you get your demestic water from the boiler) and if you have a temp valve i would bump it up to high up to 190. there is a lot of varibles to concider. that aquastat will keep your boiler running all year round. witch is good for the boiler.