Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
sno-melt insulation
jerryb
Member Posts: 113
Can anybody tell me what would be the best insulation to put under a driveway of paver's bricks?Mad Dog showed a job he did on L.I.'s gold coast i think were bricks,MD what kind of ins did it have.I'm located South Shore L.I. Thanks for any help.
0
Comments
-
Insulation under heated driveway
Use closed cell extruded polystyrene foam board such as Blue Dow Styrofoam or Pink Owens Corning Celfort. The R-value is 5 per inch of thickness. These materials do nor absorb ground water and hence retain their R-value over time. Do not use cheaper molded bead polystyrene foam board as it does absorb ground water and loses it's R-value over time.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements