Hydronic heat when no is no water in the building.
Paul_26
Member Posts: 3
I've got an artists studio going up that has no water in the building. I'd hate to put in warm air heating, but the no water thing is a problem. Any ideas?
0
Comments
-
use another expansion tank as a reservoir0 -
How big (per sqft or per system volume) & how long between refills & repressurizations?0 -
NO problem.......
how far away is a hose bibb? Or in worse case scenerio can you get 30,40 ,50 gallons to the site? Use a pony pump to purge /fill and /or Run the hose(s) from the hose to the boiler to fill/purge and them stick 1 or 2 Low water cutoffs on the boiler....I have done it as have others....no problem....kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
If it's a closed.....
system and all hot water heating system should be...there should be no need to repressureize, really.If there is a need to, more than once a year or so, you could very well have a leak...thats where the LWCO comes in.kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
LOOK AT AXIOM. SMALL PACKAGED AND 50 GALLON AUTOMATIC MAKEUP TANKS. VERY NICE PRODUCT. EVEN A SMALL 5-10 GALLON SIZE0 -
Thanks to ME....
I did this for a cabin that is not occupied for long periods of time....diferent reason, same result.0 -
Newly commissioned hydronic
systems will burp air for a few days, or more. Depending on how well you can purge it at initial fill.
You will need some additional make up water to replace purged air. If you have, and you should, a low water cut off switch, your system may shut down if the system burps air and does not have a refill system.
Is this temporary, or will the building never have a water supply? If never, I would look into an auto fill system like described, or an Axiom filler.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
We do that on EVERY new job...
It's the only way we could get insurance. I'd also recommend a low pressure cut off in addition to the low water cut off.
Can't be too safe when you don't have a make up to fall back on...
ME0 -
No water in the building
What you describe is pretty much what we find in every boiler installation in that we almost never connect the domestic water system to the hydronic system.
In our part of the country, domestic water is always from a local well, and is full of minerals, so we bring in deionized water for the boiler fill. The only time we use well water is when we do a pre-flush with cleaners, and then we blow it all out (as much as possible) before filling with the DI/propylene glycol mix.
So long as there are no leaks in the system, and we have done a very thorough purging of air, pressure loss in a year's time is negligible. In an average house, a quart or two of make-up water after the first year of service will take care of bringing the pressure back up to 15 - 20 psi.
As other posts have advised, a LWCO is essential with such a system.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements