LWCO & Oil fired HWH

Dan Peel
Dan Peel Member Posts: 431
Does he now own a LWCO ? ..... Dan

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=174&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>

Comments

  • sootmonkey
    sootmonkey Member Posts: 158
    LWCO & Oil fired HWH

    In Maine, the code now states that ALL installed boilers shall have a LWCO installed. Now think about this. An oil fired hot water heater with no pressure guage and no LWCO. I went to a call last winter to clean the HAF & the HWH. The home owner is away, as this is his "summer camp" (palace on the water) The H2O pump has been shut off and the domestic plumbing has been drained, including the HWH. Just by my bubbly personality the caretaker desided to kill so time and come in with me. After I finished with the Thermopride, I started on the oil fired HWH. In conversation it came up that everything had been drained. WOW!!!, Man I would have fired it. Wouldn't have Known. signed Dumb Sootmonkey
  • Al Letellier
    Al Letellier Member Posts: 781
    lwco and HWH

    > In Maine, the code now states that ALL installed

    > boilers shall have a LWCO installed. Now think

    > about this. An oil fired hot water heater with no

    > pressure guage and no LWCO. I went to a call last

    > winter to clean the HAF & the HWH. The home owner

    > is away, as this is his "summer camp" (palace on

    > the water) The H2O pump has been shut off and the

    > domestic plumbing has been drained, including the

    > HWH. Just by my bubbly personality the caretaker

    > desided to kill so time and come in with me.

    > After I finished with the Thermopride, I started

    > on the oil fired HWH. In conversation it came up

    > that everything had been drained. WOW!!!, Man I

    > would have fired it. Wouldn't have Known. signed

    > Dumb Sootmonkey





    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • Al Letellier
    Al Letellier Member Posts: 781
    lwco & water heater

    It's been law in Maine since 1973 that all boilers have LWCOs. Not required on water heaters. Guess it shows one has to be very careful to check for flow before firing them.
    Thanks for reminding us not to take everything for granted.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"