PA404
dk_4
Member Posts: 4
Is it the 1# face to me, or the 1 # align to the side mark?
dk
dk
0
Comments
-
PA404
I would like to ask how do I set the differential wheel of PA404 to 1 psi? the dial # face to me or face to the left side, asuuming standing in front of the Pressuretrol. thanks in advance.
dk
0 -
The cut-in is on the face. Set the cut in to .5 using the screw on top and in the inside under the cover there is a wheel . The wheel is the differential , cut -in + Diff. = cut-out . in a normal home or small building you would set the diff to 1# , yes this will give u 1.5# lowest setting on a P4040 -
pa404
the number on the wheel facing you
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
And then it will still
make 4 psi. ;-)Retired and loving it.0 -
404
If its a heating boiler the PA404 "A" model is the one. To set the differential remove the cover and turn the wheel to align with the mark. As the others said set the outside cut in to as low as it will go.0 -
My PA404 doesnt use a wheel--cut in and differential are each adjusted via screws on top. Also, the scale plate for each can be moved up an down about 1/4 inch--how do I figure out what right settings are? PS. My PA404 is about 50 yrs old...0 -
Ain't that the truth. Recommend a better control?
I made 3.5-4.75psi with my old PA404.
I make 3-4psi with my new PA404.
Both were set to 0.5+1.
What do I do? L404? Vaporstat?
Mark0 -
Not an L404A?
(vs. PA404A) also honeywell, w/ two top adj screws, diff (subtractive) and main (cutout) scale on the front and a mercury switch?
0 -
using a manometer
attached to the boiler drain in accordance with Noel's instructions, I found that in order to have the vaporstat cut out at 8 ounces of pressure, the dial setting had to be lowered to about 5.5 ounces of pressure. There is no doubt that lower is better. Cut in dial seems to be okay.0 -
Nope. It reads PA404A1X05 on the casing. It does have mercury float. Scale is from 0-5 psi on cut in and 0-6 psi on differential...0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements