How many BTU's
Jamie_6
Member Posts: 710
What is the maximum amout of BTU's you can squeeze out of 3/4" pipe?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>
0
Comments
-
Rule of thumb
Jamie, usally I use 40,000.
Scott
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
Depends!
Using the Pipe Sizer module of Siggy's Design Studio. If you want to push to the limit!
170° average water temperature, 20° delta T, 6.4 gpm, 4fps would move 62,000 BTU/ hr. (7.2' per 100' of tube pressure drop)
4 feet per second is the high side for velocity.
If you can spread the delta T the number increases.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
what length?
hot rod, what length of 3/4 are we talking about?0 -
that is for
100 feet of tube. This Hydronic Simulator Module lets you build the circuit and include fittings and valves, as well as emitters. Only then will you get a complete pressure drop through the system.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
That's for 100 feet
The Hydronic Simulator Module allow you to build the entire piping adding valves and fittings. It also shows flow rate and pressure drop for the entire assembly.
This example shows 50' of baseboard, 100 feet of 3/4, 10 ells, 2 ball valves and a flow check.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
Sweet program HR! We'll have to look into that. I know it was such a broad question. I'm looking @ running HePex to a water coil about 100' away (oneway) from my boiler. The hot-water coil needs 8 gpm @ a .31 friction loss to provide about 85,000 btu's and we have to use a 30% glycol mix.
Jamie
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
A bit of difference between pex and CU
Regular pex has a smaller ID (SDR-9) than copper. You could proably squeeze by with 1" HePex
85,000, 20°delta T, 170°average temperature, 8.9 gpm, 30% glycol, 4" head per 100' at 4.7 fps, using 1" pex.
I-1/4" pex at 3.1 fps would be better but the 4.7 fpm proablby would not pose a problem. b4 fpm is generally max.
Generally the HePex would not have a lot of fittings, if any. I'd use the 1".
Be sure to insulate a long run like that. You could easily lose 15° before you hit the fan coil!
If you go to www.hydronicpros.com and download the demo you can try some options with the Pipe Sizer.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
beware the fittings
1" is tough to work somtimes and it's really appealing to stick in a few pro-pex fittings. be careful, they eat up pump head really fast! having done this a couple of times now, I will solder ftg x pex adapters into long radius elbows in the future, and keep my head loss in line. and if anyone from wirsbo is out there - work up a metal bend support for the 1". Paul0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements