Gravity hot water boiler
Butch_2
Member Posts: 8
Hi all, I work in maintenance and believe that I can install a boiler. I have a question. I have this old (35 year old)gravity hot water boiler (for heating only, no domestic hot water) with 2 supply lines and 1 return. First off, do they still make gravity boilers? Secondly, would I be better off just installing another gravity system or converting to one that has a circulating pump? Any info would be greatly appreciated.
Thanks, Butch
Thanks, Butch
Difficult (if not impossible) to find a modern boiler with tappings of sufficient size. You'd probably be better off converting to forced flow.
If you DIY, PLEASE have your work reviewed unless you already work with combustion appliances regularly--and I don't mean just replacing water heaters now and then.0 -
gravity system
It's pretty tough to beat an old gravity system that's installed correctly and working right. If you system is like that, both Buderus and Viessmann make excellent boilers for gravity installations. Other than the lack of zoning capabilities, gavity systems work great and are quite efficient. Look carefully before you leap.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
THANK YOU FOR YOUR INPUT GENTLEMEN. SOUND ADVICE! SO WHAT YOU ARE SAYING IS THAT I AMY HAVE A HARD TIME FINDING FITTINGS FOR A NEW INSTALL OF A GRAVITY SYSTEM?0 -
Some other gravity boilers
I believe Burnham has one and probably the Weil Mclain EG series (all three inch tappings). If you look at steamers, you may find more boilers with the large tappings you need.
Boilerpro0 -
From a boiler mfgr.
"You really do not want to pipe the system directly through a new boiler. You would be much better off setting up a primary secondary injection system whereby your current return(s) would connect directly to your supply(s)
and the boiler could be connected into that piping with 2 tees close together with a pump to inject into the system.
If equipped with a Tekmar variable speed injection control, this setup will perform well and the boiler will be protected by means of a return water sensor."
You essentially have to join the return(s) to the supplies(s) with a BIG pipe in a manner that ensures good gravity flow and put a little injection system from the boiler into closely spaced tees in the big pipe. Obviously you want the direction of the injection to be the same as the direction of gravity flow so you would put the supply tee from the boiler lower or downstream and the return tee to the boiler higher or upstream.0
- 86.5K THE MAIN WALL
- 53 Biomass
- 95 Chimneys & Flues
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 41 Industry Classes
- 48 Job Opportunities
