Went to a call today that we were at last week. Customer has one bathroom that has a hot water problem. Only in the winter. Our tech that went there last week saw that one zone was not wired into the reverse, just a straight RA832. So he told them to turn down this zone for a half an hour before a shower and see if it works better..if so we will do some re-wiring. Well today I went and did the annual service on this oil boiler with a domestic coil. The HO said the trick didnt work. So why would the hot water to this bathroom only be a problem in the winter if it has nothing to do with the improperly wired zone? Also does anyone know if a L8124 can handle a RA832 relay and Taco007 on the ZR/ZC terminal?

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=280&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"</A>

Comments

  • flange
    flange Member Posts: 153


    my guess is that your coil is full of lime/rust/whatever. during winter, city water is much colder entering that coil, and you see reduced heat transfer due to the scaling. might be time to pull the coil.
  • Paul Mitchell
    Paul Mitchell Member Posts: 266
    I agree but

    They have another bathroom and two other sinks that do not experience the problem. So they say.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • It is just one bathroom

    that is affected ? The shower and the sink ? Are there other showers in the home that work fine ? If it's just the one shower , is it one of those old style high flow showers ? I had the same problem last year on a new install where the shower would run cold in 5 minutes . It didn't help that it was running at 6 gallons per minute . Also , like Flange said , the water coming in is much colder than normal which decreases the output of hot water .

    It's been a long time since I installed an RA832 , but I believe it has the 1,2,3,4, T T , and X X terminals ? Are there a 5 and 6 terminal also ? In the past , if we were hooking in a small zone to an existing boiler , we would power the relay from ZC of the aquastat . It will at the least shut down the added zone if the temp drops below the low limit . Not the best way to do it though .
  • Paul Mitchell
    Paul Mitchell Member Posts: 266
    ron jr

    Yes only one bath affected, Only shower as far as I know, Other showers work fine. Could be a flow thing but why ok in the summer?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • Jamie_6
    Jamie_6 Member Posts: 710


    Maybe they just take cooler showers in the summer and don't notice it?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • Gotta be sure

    about the flow at that shower and the others . I went back to our problem job and timed how long it took for the temp to drop in the shower . Then I measured the GPM by filling a 5 gallon pail from the shower while timing it . I did that at all 3 showers , it took a long time . I had to wait between each one for the indirect to heat back up ( Yep , a new Burnham V84 with a 50 gallon Megastor ) . This was when the temp outside was in the single digits for a week or so , and the water temp coming in was alot lower than normal , with the pressure being very high .

    Is the problem that they have no hot water at that shower in the winter or that it runs cold after a short amount of time ? If it happens only in winter it doesn't sound like a flow problem , but thats just a guess . Is it a single lever shower ?
  • Paul Mitchell
    Paul Mitchell Member Posts: 266
    ron jr

    double lever shower...and they have to let the hot water"trickle" to keep it there.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • Paul Mitchell
    Paul Mitchell Member Posts: 266
    good point

    could be as easy as that...some things are not so technical.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
  • Frank_17
    Frank_17 Member Posts: 107


    chances are it's a delta faucet right?souds like you need new guts to it.
  • joe_14
    joe_14 Member Posts: 138
    832



    paul if i remember right a ra832 is jumped internally to provide power to contacts 4 and 6. will not work correctly with zc and zr. you need to change the control to a taco501 or a honeywell 845. these will work fine with zc and zr.



    good luck

    joeg.