I am going to pour a 7 ft. by 13 area in my basement I want to install the radiant floor heating to experiment with before I do the rest of my house. I bought 100 f roll of half-inch white pex cross - linked tubing from Lowes and fittings. Is this the right stuff? all the pictures I've seen online use red tubing. I read where it needs an oxygen barrier tube instead? There are no contractors listed within the hundred mile radius of your contractor search. Mike
0
Comments
-
Non barrier
pex can be used, IF you make sure all the piping and components are non ferrous. Copper, brass, or bronze, stainless, plastic, etc
I use non barrier on some large jobs with stainless steel boilers and bronze pumps and purgers.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
color does not really....
mean a thing...you really should have a oxygen barrier unless you plan on seperating the tube w/ a heat exchanger and or use NO ferrous parts on the radiant and boiler. Tube must be marked as having an O2 barrier.(german din std4726). Insulate under your slab well. I can't believe there are not good contractors where you are. Look around, ask for references and job pictures. good luck. kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
Would this include a galvanized pipe heat exchanger in my woodstove firebox? Mike0 -
Nope
You would be doing yourself a favor if you added a plate heat exchanger and used a bronze pump on the radiant side.
Good luck!
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
careful w/ wood...
heat. temps can really run away on you. maybe a storage tank and a good mixing valve would be a must. kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
I plan on a 500 gal. storage tank and separating the domestic water heating tank with the copper coils inside the storage tank. Mike0 -
Good
but you still need to isolate the radiant from any ferrous materials.
That Pex you bought has no O2 barrier.
A plate HX with a bronze pump is the way to go here.
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
What is a plate heat exchanger? Mike0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements