oil tanks

Anthony D.
Anthony D. Member Posts: 63
Need to install (4) 330 Gallon indoor tanks in a commercial building. Not sure of the best way to install the tank Fill & Vent piping, and the supply and return to burner.

Can someone point me in the right direction?

Thank you.

Comments

  • Dana
    Dana Member Posts: 126


    Look in the oil code for your State.
  • Andy Morgan_2
    Andy Morgan_2 Member Posts: 147
    I like

    To run separate fill pipes, and to tee the vents together, with vent alarms in each tank. All 2 inch black with swing joints.I never liked to crossover deal. Then tee the bottoms together and run a single line to the burner. Line size depends on a few different factors. The fuel pump spec sheet will tell you this.

    Andy Morgan

    R. Morgan Mechanical, LLC
  • Andy Morgan_2
    Andy Morgan_2 Member Posts: 147
    Re read the message

    Look in the code books, I am not quite sure, but I don't think that amount of storage is allowed inside a building.
    I read it as two tanks!

    Andy Morgan

    R. Morgan Mechanical, LLC
  • lchmb
    lchmb Member Posts: 2,997
    just a suggestion

    Not to sound bad..but you do not sound to be someone who is familier with the code's related to oil in your state..although it may cost a little more in the long run, I highly suggest you contract to a proffesional in your area...not only will it get done legally..it will be his back busting to get them in...
  • Bill Nye
    Bill Nye Member Posts: 221
    NFPA-31

    NFPA-31 is where you want to look. I have 2001 edition at hand. I am looking at page 31-18,31-19.

    660 gal max capacity. Section 7.5 . You can store more oil if you have 2-3hr fire rated walls and special construction
  • Patrick Powers
    Patrick Powers Member Posts: 40
    Roth

    Look into Roth they have a nice setup for mutiple tanks. What ever road you take look in local codes and hire a pro you can very easily have a real mess if it is not done properly.
  • Anthony D.
    Anthony D. Member Posts: 63
    The way I read it Bill..

    > NFPA-31 is where you want to look. I have 2001

    > edition at hand. I am looking at page

    > 31-18,31-19.

    >

    > 660 gal max capacity. Section

    > 7.5 . You can store more oil if you have 2-3hr

    > fire rated walls and special construction



  • Anthony D.
    Anthony D. Member Posts: 63
    The way I read it Bill..

    ..is you are not allowed to use a "single" tank of more than 660 gallon, but you can use multiple tanks upto a maximum storage of 1375 gallon. (See 7.5.13.1)

    Ands if you read 7.5.13.2 if the tanks are separated by the 2 hour wall you can have upto 1375 gallon in each area.

    Both these senarios are when tanks are not in a dedicated room.
  • Anthony D.
    Anthony D. Member Posts: 63
    According to the NFPA31

    It looks like I can install upto 1375 gal. maximum (according to NFPA31 page 31-19 / Section 7.5.13.1,)as long as no single tank exceeds 660 gal.
    Since this is an indoor tank installation I chose to use 330 gal. tanks.
    But the code book only shows a pipe hook-up for a two-tank set-up. There is an illustration for more tanks, but only for listed or engineered fuel storage system.

    I don't want to run four seperate fill lines if I don't have to, maybe I could pipe two tanks as shown in figure 7.5.15, and do this twice. Then common the vent lines, using one vent alarm per two tank combo.

    Sort of a hybrid between what I was thinking and your original advice.

    any suggestions?
  • Anthony D.
    Anthony D. Member Posts: 63
    what makes you...

    ...think I'm not familiar with codes or a professional in this industry?
  • scrook_2
    scrook_2 Member Posts: 610
    the wording

    of your initial question on fill/vent/supply/return plumbing. It can be interpreted anywhere from lack of familiarily w/ any oil tank plumbing requirements to just a lack of familiarity w/ requirements for requirements for setting up more than a pair of tanks. It is also not clear if you are in a state with very strict & specific codes/requirements for oil tanks or one that only has some basic requirements. No question is a foolish question, better to ask and learn!

    You also might try http://oiltechtalk.com/ the "discuss" page for more input for your locality.

    Stay out of the hot sun! (especially if your in N.E.)!

  • Anthony D.
    Anthony D. Member Posts: 63
    I may not have been

    clear on the question. My question was on the proper way to interconnect multiple tanks. I have worked with many oil systems over the past 20 years, but have never had to replace/install multiple tanks.
  • Firedragon_4
    Firedragon_4 Member Posts: 1,436
    You cannot put in more than 660 gallons

    and connect it to a single burner unless you have an 'engineered' or 'listed' system, FACT!
    NFPA31-2001

    Be careful of 'sales claims', they don't hold up in court, BIG FACT!
  • Anthony D.
    Anthony D. Member Posts: 63


    Thanks for the advice, but what about when you are supplying six boilers in various locations, with the use of tranfer pumps and auxillary tanks.

    What if I connect them so two 330 tanks feed two or three boilers and the other two to feed the rest?
  • Anthony D.
    Anthony D. Member Posts: 63
    According to 7.5.13.1

    you can not install an "individual" tank exceeding 660 gal., but you can have a multiple tanks upto 1375gal..

    I do see what your saying in 7.5.15.1, but I not supplying only one appliance.
  • Firedragon_4
    Firedragon_4 Member Posts: 1,436
    The drawings in the appendix sum it

    up a lot beter than time and space will allow here.
  • Anthony D.
    Anthony D. Member Posts: 63


    Thank you, I'll check it out.