Condensation in Boiler Flue
I'm getting quite a bit of condensation it the double-wall boiler flue of my in-floor heating system. Am I running the boiler wrong at 16psi and 120 degrees F?
  • kf_2
    kf_2 Member Posts: 118
    condensation
    16 PSI is probably not the problem, but depending on the type of boiler the 120 F. temp certainly could be. If it is a cast iron or steel boiler I would be more concerned with the condensation you are, no doubt, forming on the fire side of your heat exchanger.
    What kind of boiler is it?
    kf
  • Any idea what your
    return water temperature is. If it is very low and I assume it is if you are running at 120 degrees then you are probably also condensing in the boiler.
    You need to run the boiler at a higher temperature and then temper water to the system, then in turn the return water will still be low but you can have a bypass connected to the system to take care of that.
    Some of the pro's here on the Wall will give you a possible set up for what to do. Please give a little more info about your boiler and system to help them help you.
  • hr
    hr Member Posts: 6,106
    You need
    to address that soon. Those temperatures will quickly eat away the aluminum liner in you B-vent system.
    Conventional (non condensing) boilers need to operate above the fuel dew point. Somewhere in the 130°F range, foe natural and LP gas..
    Damage to the heat exchanger will also occur, the flue pipe seems to take the brunt of condensing temperatures first.
    You need a method to run the boiler temperature up, mix down for you system requirements. AND provide a means to watch and respond to low return temperatures to the boiler.
    Sounds complicated, but doesn't have to be :)
    Plenty of electronic and mechanical means to get there :)
    hot rod